John DeBruyne
REGISTERED
Goal: To determine if the two side-by-side apartment structures are their own "buildings".
Existing 3-story 12-unit side-by-side apartment structures that we are assuming were constructed at the same time in the 1970's. Type V-B construction (wood-framed with wood trusses) with the primary structural members parallel with the shared side-by-side walls which makes each structure structurally-independent of each other. The shared wall is comprised of two rows of 2X4 studs, not connected and not sharing base/top plates... you could pull one structure down without affecting the other structure.
Existing 3-story 12-unit side-by-side apartment structures that we are assuming were constructed at the same time in the 1970's. Type V-B construction (wood-framed with wood trusses) with the primary structural members parallel with the shared side-by-side walls which makes each structure structurally-independent of each other. The shared wall is comprised of two rows of 2X4 studs, not connected and not sharing base/top plates... you could pull one structure down without affecting the other structure.
- Would the side-by-side walls be considered exterior walls for each structure? If we are trying to make them individual buildings, I think "yes", therefore Section 705 applies.
- 705.5 says to refer to Tables 601 (0-hour) and 602 (1-hour) for fire separation distance <5 feet.
- Where is the correct positioning of the fire rating? Options 1, 2 or 3 (or something I'm not considering) per the attached sketches.
- The side-by-side walls to do not extend to create a parapet per 705.11 nor does it terminate at the underside of the roof deck per Exception 5.
- Is the construction simply a fire rated exterior wall, or would it fall under "fire wall", "fire barrier", etc.?