NEC 250.50 Separate Building

Does the fact that this is going to be a separate building receiving power from the service of another building? Does the fact that there will be a feeder serving this building with grounds and neutrals separated?
Those are immaterial. There is no requirement in the NEC to identify a Grounding Electrode Conductor with the color green. Conversely there is no prohibition.

Cheers, Wayne
 