Forum Coordinator
If you were to perform a final inspection and test a few receptacles and found reverse polarity, what NEC code section would you cite?
That's not going to do it, unless the Hot/Neutral Reverse is due to mismarked terminals on the receptacle. That section only regulates markings on the device; it does not regulate how you land the conductors on the device.200.10 Identification of Terminals.
Alrighty then...point us in the right direction.That's not going to do it, unless the Hot/Neutral Reverse is due to mismarked terminals on the receptacle. That section only regulates markings on the device; it does not regulate how you land the conductors on the device.
Cheers, Wayne
I don't have anything better than 110.3(B): the receptacle installation instructions will surely tell you to land the grounded circuit conductor on the silver screw. If there's something more explicit in the NEC, I didn't find it during a brief perusal.Alrighty then...point us in the right direction.
I wouldn’t. Well maybe if I were in Montana ….everywhere else it would be “Polarity is reversed”what NEC code section would you cite?
Correct. You beat me to it. Ice, you’re in the correct chapter thoughThat's not going to do it, unless the Hot/Neutral Reverse is due to mismarked terminals on the receptacle. That section only regulates markings on the device; it does not regulate how you land the conductors on the device.
Cheers, Wayne
200.11 Polarity of Connections. No grounded conductor shall be attached to a terminal or lead so as to reverse the designated polarity.Try 200.11
Close only counts with horse shoes and shotguns.Ice, you’re in the correct chapter though
There's a joke here about electrical installation being "plug and pray."110.3 (B) Installation and use. Equipment that’s listed, labeled or both shall be installed and used in accordance with any instructions included in the listing or labeling.
That would be the first electrician that ever read the installation instructions that comes with a receptacle.
And things having to do with the splitting of atomic neuclei...Close only counts with horse shoes and shotguns.
You would have to call the CO OP and let them know the crossed the wires during the installation of their equipment.Well maybe if I were in Montana