It would be doing your job.I can only imagine the trouble that I would be in if I punched holes in CMU.
I use a tuning fork.It would be doing your job.
Here are some examples. I've posted pics like this before. Click on the pics to enlarge.Not trying to downplay the omission of grout, but I don't understand several things that led to "hammer time":
1. Does your jurisdiction require deputy inspections during grouting?
2. Did it appear solid grouted when looking down from above, such that only smashing the block would reveal the void? Or was the void also visible from above?
3. Hammering the block seems like a destructive testing / last resort for verification. Were there other clues that first led you to be suspicious the cels weren't grouted? Or is this standard practice for grout inspection? (Not trying to be critical, but trying to understand here.)
And it MIGHT actually be inspected....We have a special inspectors performing inspections during masonry construction. It might be periodic inspections.
Another name for special inspectors... usually originating from California, particularly the LA area in my experience.1) I don't know what deputy inspections means.
Yes, and how is that verified?And in Cali ALL cells are normally called out to be grouted solid - not just bond beams and certain verticals.
2) I don't know, I arrived after the fact.
3) If it was grouted as required by the plans, it would not be destructive. This is standard practice to make sure they did not block the cells to save concrete.
Apparently the inspection paid off. Normally the bottom block are chipped out, inspected for rebar, then covered with plywood and then removed after the concrete is poured. Normally you don't find this stuff unless inspection holes are missing or were missed during the pre-fill cell inspection.
https://www.ladbs.org/docs/default-...pection-ib-p-bc2011-035.pdf?sfvrsn=198eb53_52Yes, and how is that verified?
Pounding on the wall with a hammer is apparently an accepted practice in Jeff's jurisdiction. If that were done anywhere that I have worked, there would be a valid complaint. If I had a reason to suspect that the cells were not filled, I would resort to a 1/4" drill bit and even that would raise eyebrows.OK, so on this kind of project, the CMU is not the finish surface of the wall; it will get covered with some other finish in the future; thus, hitting it with a hammer for purposes of inspection has no detrimental effect on the finish surface of the wall.
Is this correct?