There is no doubt to me that the engineering and execution of the work for the embedded anchor rod is the Achilles heel of this system. Who is seeing this in their area? This goes beyond seismic and is very relevant for wind loads.
Such as mine where my jurisdiction is an an ASCE 7 Exposure D 169Vmph zone.While wind loads are considered global wind uplift tied to foundation is seldom considered. It probably helps that we do not have the hurricanes and tornados common to other states.
I see these used all over the country. QA/QC does not seem to be a problem. Are you seeing failures? I have not.There is no doubt to me that the engineering and execution of the work for the embedded anchor rod is the Achilles heel of this system. Who is seeing this in their area? This goes beyond seismic and is very relevant for wind loads.
I don't think the failures will be seen until there are high winds or seismic events.Are you seeing failures? I have not.
Many times frame walls don't have enough dead low to overcome the uplift by I think the only rods at work are the ones that have springs and retention themselves when the wood shrinks. I try not to design wood structures to resist high wind loads as there's thousands of areas that can be deficient. Sometimes you can pull the rod connection right out of the slab because it hasn't been prepared properly.I see these used all over the country. QA/QC does not seem to be a problem. Are you seeing failures? I have not.
These systems (there are many) are used where you have net uplift. Engineers try to design their shear walls where they have enough dead load to counteract the overturning but it isn't always possible or economical. These systems solve the overturning issue.
I think similar systems (such as Z4 by Mitek) have been around long enough that they have worked as designed during actual seismic events.I don't think the failures will be seen until there are high winds or seismic events.
Thirty years ago I was a carpenter on a five story wood hotel at Sacramento Ca. At the elevator shaft was a group of all-thread rods for a brace. The rods were the largest that I had seen in use... probably close to 2"dia. There was a plate and nut at the bottom.Sometimes you can pull the rod connection right out of the slab
Yes that's when the failures occur as I have seen many many pull-outs in hurricanes and tornadoes. I have also seen CMU Bond beans ripped out too.I think similar systems (such as Z4 by Mitek) have been around long enough that they have worked as designed during actual seismic events.
Yes but unfortunately most rods have no provisions for wood and building shrinkage and become loose but I guess it's better than nothing. When I didn't inspections five or six years later on rodded structures once the wall was open I can move the rod around 4 in. There should be an access hole so you can tighten the coupling or have a key way for a hex wrench.Thirty years ago I was a carpenter on a five story wood hotel at Sacramento Ca. At the elevator shaft was a group of all-thread rods for a brace. The rods were the largest that I had seen in use... probably close to 2"dia. There was a plate and nut at the bottom.
When it came time to frame the brace it was discovered that the rods were not sticking out of the concrete far enough. No problem, they are after all, threaded.
Yes that can be a problem so you can use a couple studs nailed together and strapped top and bottom to act as a tension tie.The systems I've seen here in California are like the ones you've described in post #6, with springs that ratchet the system tighter as the wood shrinks.
Two months ago we did a remodel on a 15 year old building, and discovered one of these where it didn't show up in the owner's record drawings.
Despite all the years of building shrinkage (and despite the studs not having a "KD-19" stamp on them), the spring had done its job and the rod was not loose.
By the way, that does point out one downside of using rods vs. holddowns: it's really had to engineer a workaround if you need to move a wall during a remodel, without affecting an entire stack of apartment units.