Forum Coordinator
What is the difference in the IMC between Domestic Kitchen Exhaust and Commercial Kitchen Exhaust?
Yes, but what separates the requirement? IMC 917?A lot
Domestic Section 505 Commercial Section 506 & 507
The use classification of the space the kitchen is located within. I.e. domestic would be "R" use classifications, and commercial would be any others.What is the difference in the IMC between Domestic Kitchen Exhaust and Commercial Kitchen Exhaust?
A break room is not a commercial kitchen. “Commercial“ implies enterprise centered around food.So what if you bought a GE residential electric stove and installed it in the breakroom of a commercial office building?
917.2 Domestic appliances.But the listing of the appliance would be key here
Yes, but in order to determine the type of exhaust, you have to determine if it is a commercial kitchen or not. If the appliance is listed for commercial use only, its a no brainer. Commercial kitchen, commercial exhaust system in accordance with IMC 506 and 507.I thought we were talking exhaust...? But the listing of the appliance would be key here....If they only allow it in residential uses, NG in the breakroom....If they allow it in "similar to" residential use, might be OK...
BINGOYes, but in order to determine the type of exhaust, you have to determine if it is a commercial kitchen or not
Ranges listed for residential use usually say something along the lines of "approved for use in residential applications" but don't limit their use to residential. Unless the instructions or listing is worded in a way that somehow prohibits use in commercial applications, its allowed. Listed commercial ranges are typically pretty clear in the instructions and usually right on the nameplate that they are to be used in commercial applications only.But does the "residential" listed appliance allow it in a commercial building even if the IMC does? Or does it void the listing?
You are a meanie.If they are only approving it for residential, then that is all I am going to allow...
Sometimes...The manufactures just need to get their language in line with code.....Lord knows they pay enough lobbyists to make code changes...You are a meanie.
And a range doesn't have a flue....A low heat (residential) appliance is not a piece of equipment by definition.
EQUIPMENT. Piping, ducts, vents, control devices and other components of systems other than appliances that are permanently installed and integrated to provide control of environmental conditions for buildings. This definition shall also include other systems specifically regulated in this code.
APPLIANCE. A device or apparatus that is manufactured and designed to utilize energy and for which this code provides specific requirements.
Low-heat appliance (residential appliance). Any appliance in which the products of combustion at the point of entrance to the flue under normal operating conditions have a temperature of 1,000ºF (538ºC) or less.
Given this scenario, is makeup air required? 505.4, and logic would seem to say yes, but this section really seems geared towards the dwelling unit application. I have a classroom with 3200cfm of domestic cooking exhaust and the room is already slightly negative between supply and return, with no makeup air.A high school life skills class would also be domestic. They're teaching kids how to cook for themselves at home.