jar546
CBO
In accordance with accessibility standards, accessible unisex toilet rooms cannot replace multi-user toilet rooms, except in cases where it is not technically feasible to make multi-user rooms compliant, particularly in alterations. Both types of restroom facilities must be provided when multi-user and unisex restrooms are required. This approach is beneficial for individuals who require personal care assistants of the opposite sex.
The International Building Code (IBC) mandates the inclusion of accessible unisex or "family" toilet rooms in assembly and mercantile occupancies when six or more toilet fixtures are needed. These rooms must meet specific requirements outlined in the ADA Standards, including privacy latches and a limited number of fixtures.
Additionally, the location of toilet rooms is addressed in two scenarios:
The International Building Code (IBC) mandates the inclusion of accessible unisex or "family" toilet rooms in assembly and mercantile occupancies when six or more toilet fixtures are needed. These rooms must meet specific requirements outlined in the ADA Standards, including privacy latches and a limited number of fixtures.
Additionally, the location of toilet rooms is addressed in two scenarios:
- In multi-story facilities exempt from vertical access requirements between stories, a toilet room must be available on a story connected to an accessible entrance through an accessible route. Other stories' toilet rooms must also comply with accessibility standards.
- During alterations where making men's and women's rooms compliant is technically infeasible, an accessible unisex toilet room can serve as an alternative if it is situated in the same area and on the same floor as the existing toilet rooms.