Yes, I agree. We an only make decisions based on what we see and know, not what might be.I'm unclear on whether the unit has an integral thermal protector or other integral overload device;
So then I'd read the right half of the label before making a decision. : - )Yes, I agree. We an only make decisions based on what we see and know, not what might be.
Great. So the phrase of interest is "This ventilator should be installed with remote motor-overload protection when 3 phase or 2HP or larger single phase motors are required."I don't want you to make hasty decisions, so I went back on the roof today just for you.
36.8 A ventilator having one motor with other loads or more than one motor with or without other loads shall be marked with one of hte following:
a) The minimum circuit size and maximum current rating of the overcurrent-protective device unless both are 15A or less; or
b) The rating of the largest motor in volts and amperes, and the rating of any other loads in volts and either amperes or watts.
Exception: The current value of a motor rated 1/8 horsepower (93W output) or less, or a nonmotor load 1 ampere or less may be omitted unless either load constitutes the principal load.
36.5 A ventilator that incorporates motor-overload protection shall be marked to indicate the presence of such protection.
36.6 A ventilator that does not incorporate motor-overload protection shall be marked:
a) To indicate that the ventilator should be installed with remote motor-overload protection; and
b) To provide such motor-rating data--voltage, frequency, horsepower, and full-load current per phase--so that proper protection may be determined.
Great. So in the real world when an electrical inspector has 24 inspections in 18 different locations and 8 hours to do them in, he or she will fail the inspection if the contractor does not have a 15A OCPD in place and instead uses a 20A, OR they won't care and will just pass it as this really does not make a difference in the grand scheme of things until there is a roof fire and an expert witness uses the label against the contractor and inspector for negligence.I.e. if the ventilator has motor-overload protection, as I infer, then the requisite 36.5 marking is missing. Whereas if it doesn't, then the requisite 36.6(a) marking is missing, as the label references that only for 3 phase and 2HP or larger single phase motors, which this unit does not have.