Changes in the 2024 International Building Code (IBC)
The 2024 International Codes® (I-Codes®) have undergone substantial formatting changes as part of the digital transformation strategy of the International Code Council® (ICC®) to improve the user experience. The changes, promoting a cleaner, more modern look and enhancing readability and sustainability, include:
  • Single column text format and modernized font styles improves readability
  • QR Codes replace vertical margin sidebars and arrows to identify code changes more accurately
  • Shading for table headers and notes improves locating tables and applicable notes
  • Grouping of associated content brings tables and figures immediately after the parent section
  • Users have capability to validate authenticity of their book and register it with the ICC to receive incentives.
The 2024 IBC® applies to all buildings except detached one- and two-family dwellings and townhouses up to three stories. The 2024 IBC® contains many important changes such as:
  • Duties and powers of the building official: an overall reformat of Section 104 regulating duties of the building official, the approach for reviewing for code compliance has been significantly updated to reflect the current manner that alternate materials, designs and methods are evaluated.
  • For the first time ever, the 2024 IBC includes provisions for tornado loadings.
  • Updated wind, earthquake, and snow loads.
  • The updated design rain loads are now based on the summation of the static head, the hydraulic head, and the ponding head.
  • Updates to Risk Categories including Photovoltaic (PV) panel systems and facilities providing power generation.
  • Updated and expanded provisions for Temporary Structures.
  • New provisions regarding the wind resistance of aggregate-surfaced roofs.
  • Roof Coverings: Updated provisions for underlayment.
  • New special inspection provisions for metal building systems.
  • New provisions for structural concrete reinforced with glass-fiber reinforcement.
  • Concrete: To improve ease of use, Chapter 19 on Concrete has been Updated and reformatted.
  • Masonry: TMS 402 and TMS 602 references have been updated to the latest 2022 editions.
  • An increase in the allowable height of a Group R-2 occupancy building with a NFPA 13R sprinkler system.
  • Occupiable space requirements now apply if a roof is usable for anything more than maintenance or repair and occupants must have access to multiple egress options from a story based on the occupant load and the story requirements.
  • Adult changing tables are now regulated where they are provided and are also required in large assembly and mercantile, college lecture hall/classroom buildings and highway rest stops.
  • Fire-resistance-rated Wall Continuity: Updates on how supporting construction for exterior walls is to be fire-resistance-rated, especially in the case of a parapet.
  • Openings in Shaft Enclosures: Additional exceptions are provided for shaft enclosures, including new allowances for openings and penetrations.
  • Carbon Monoxide Detection: Carbon monoxide (CO) detection is now required in all occupancies where a CO-producing device is present. Detection and notification can be addressed in several ways.
  • Vapor retarders: Several updates have been made to the vapor retarder provisions for consistency with the IRC and IECC. The changes also provide additional options and better guidance for allowable types and locations of permitted vapor retarders.
  • Vertical and lateral Flame propagation compliance methods: Clarification has been provided as to when testing in accordance with NFPA 285, related to vertical and lateral flame propagation, is required. Previously this information was scattered in a variety of locations within Chapters 14 and 26.
  • New Appendix P sets forth the scoping limitations and technical criteria for sleeping lofts that are provided within Group R dwelling units and sleeping units.
Hopefully they got rid of this restriction on height.
903.3.1.2 NFPA 13R sprinkler systems​
  1. 2.The floor level of the highest story is 30 feet (9144 mm) or less above the lowest level of fire department vehicle access.
  2. 3.The floor level of the lowest story is 30 feet (9144 mm) or less below the lowest level of fire department vehicle access.
The number of stories of Group R occupancies constructed in accordance with Sections 510.2 and 510.4 shall be measured from grade plane.