I am not as familiar with NFPA 101 as I am with the IBC, and I am now faced with a project that requires compliance with NFPA 101 (2021 edition).
The project is a two-story office building and per the IBC (2021 edition), two-story stairways are permitted to be unenclosed provided the travel distances from the second story to an exit on the level of exit discharge is within the 300-foot limitation (the building is sprinklered throughout). However, I cannot find a similar provision within NFPA 101.
Section 38.2.4.1 requires "Not less than two separate exits shall be provided on every story." However, there are provisions that permit single exits or single means of egress from a room, area, or story:
Also, I should point out that NFPA 101 does not have a definition of an exit access stairway as the IBC does, nor do they describe an exit access stairway anywhere other than in Section 38.3.1.1(4). NFPA 101 does allow "convenience openings" per Section 8.6.9 but states "Such openings shall not serve as a required means of egress," which I interpret as no exit access stairs are permitted.
Has anybody come across this situation before? If so, how was it handled or accepted?
Section 38.2.4.6 allows a single means of egress for a two-story building but includes a 100-foot travel distance limitation from any point to the exit discharge. Notice that it states "means of egress" and not "exit." This is considered an "exit access stairway" as mentioned by Section 38.3.1.1(4). There is no provision for two "means of egress" or two exit access stairways from a two-story building.
Section 38.2.4.3 allows a single exit, provided the travel distance is limited to 100 feet (including within the stairs) and that the stairs are no more than 15 feet in vertical height.
However, there are no provisions that address an intermediate condition where one means of egress (i.e., exit access stair) and one exit stair are provided. It seems like it is either two exits, one exit, or one means of egress -- no middle-of-the-road provision.Also, I should point out that NFPA 101 does not have a definition of an exit access stairway as the IBC does, nor do they describe an exit access stairway anywhere other than in Section 38.3.1.1(4). NFPA 101 does allow "convenience openings" per Section 8.6.9 but states "Such openings shall not serve as a required means of egress," which I interpret as no exit access stairs are permitted.