Yankee Chronicler
It's a different section number in the 2021 IBC (1010.3.2), but the code language is the same. Here's what the 2021 Commentary has to say:
It doesn't appear to include overhead doors, but it also doesn't specifically say "Yea" or "Nay." One concern with overhead doors is that the type of power operator may or may not allow manual operation if the power fails with the door in a closed or partially-open position. Residential garage doors (at least, those I've seen) require pulling a release rope to disengage the door from the opener mechanism before the door can be lifted manually. I don't think that fits the intent of this section.
For convenience purposes, power-operated doors are intended to facilitate the normal nonemergency flow of
persons through a doorway. Where a power-operated or power-assisted door is also required to be an
egress door, the door must conform to the requirements of this section. The essential characteristic is
that the door is to be manually openable from any position to its full-open position at any time, with or
without a power failure or a failure of a door mechanism. Hence, both swinging and horizontal sliding
doors that comply with this section may be used, provided the door can be operated manually from any
position as a swinging door and that the minimum required clear width for egress capacity is not less
than 32 inches (813 mm). Note that the opening forces of Section 1010.1.3 are applicable, except that the 30-
pound (133 N) force needed to set the door in motion is increased to 50 pounds (220 N) as an operational
tolerance in the design of the power-operated door. Also note that BHMA A156.10 requires a power-operated
swinging door, when without power, to require not more than 30 pounds to set the door in motion. And
BHMA A156.19 limits the force to set a power-assisted or low-energy power-operated swinging door in motion
to not more than 30 pounds (133 N).
Definitions for the different types of power-operated doors help clarify which standard (BHMA A156.10,
BHMA A156.19 or BMHA A156.38) is applicable to which type of power-operated door (see Chapter 2 for
the definitions for “Low-energy power-operated door,” “Power-assisted door” and “Power-operated door”).
Power-operated doors are required to comply with BHMA A156.10. These doors open automatically
when approached by a person or upon an action by a person, close automatically and include provisions
such as presence sensors to prevent entrapment. Low-energy power-operated doors are required to
comply with BHMA A156.19 or A156.38, depending on whether they are swinging, sliding or folding. These
doors open automatically upon an action by a person such as pressing a push plate or waving a hand in
front of a sensor. Additionally, these doors close automatically and operate with decreased forces and
decreased speeds (compared to power-operated doors). Least common are power-assisted doors,
which are required to comply with BHMA A156.19. These doors are swinging doors that open by reduced
pushing or pulling force on the door-operating hardware, close automatically after the pushing or pulling
force is released, and function with decreased forces. Power-assisted doors do not open automatically—the
operators only reduce the opening force for easier manual operation.