Sifu
SAWHORSE
- Joined
- Sep 3, 2011
- Messages
- 3,326
Recent discussion on C of O for an existing SFD to B occupancy yielded a lot of opinions. I have two more similar projects presented to me, we will treat them as one for the sake of discussion.
Given that I am of the opinion that IEBC ch. 10 does not apply to a C of O from an SFD to a new IBC regulated occupancy, I am now more confused by the fact that the C of O from the SFD is a historic building.
For the sake of this discussion, assume that it is properly designated as an historic building.
Ch. 3, accessibility applies to everything, including existing buildings, with specifics for historic buildings provided at 305.9.
-Using 305.9 a single fully accessible toilet room is required. This is provided, along with 1 that is not, but which contains a shower. Based on the only requirement being a single compliant toilet room, and that bathing rooms are not mentioned, would this be complaint?
-There is an accessible main entrance, with an accessible route from the site arrival point.
-No other mention of any accessible requirements is made in 305.9, so does everything not mentioned in 305.9 get a pass? (maneuvering clearances and kitchenettes specifically)
Ch. 5, prescriptive-IEBC 507.1 pretty much waives all of the requirements of ch. 5 (which includes 506 on C of O's) unless deemed to be a life-safety hazard, except for structural unless the CBO waives those.
Ch. 6-12 are required to be used when using the work area compliance method. 607.2 directs that "the code" applies unless waived by ch. 12. By "the code" I assume it refers to ch. 6 through 12. IEBC 1204.1 tells us that the applicable provisions of ch. 10 apply (which pick up ch. 7,8,9) unless waived in 1204, but as discussed (without a clear consensus) ch. 10 doesn't apply...what now since 7,8,9 are triggered by ch. 10? If ch. 12 can be used regardless if ch. 10 can be used, then do we still use ch. 7 through 9 and ch. 12?
When I review things like this I start from a full IBC compliance perspective, then back out what doesn't apply in an existing building, then back out what wouldn't apply in an historical building. But, this is the first bona fide historical building I have actually reviewed as a C of O. When I back everything out, it would appear very little applies.
Has anyone else done a similar project?
Given that I am of the opinion that IEBC ch. 10 does not apply to a C of O from an SFD to a new IBC regulated occupancy, I am now more confused by the fact that the C of O from the SFD is a historic building.
For the sake of this discussion, assume that it is properly designated as an historic building.
Ch. 3, accessibility applies to everything, including existing buildings, with specifics for historic buildings provided at 305.9.
-Using 305.9 a single fully accessible toilet room is required. This is provided, along with 1 that is not, but which contains a shower. Based on the only requirement being a single compliant toilet room, and that bathing rooms are not mentioned, would this be complaint?
-There is an accessible main entrance, with an accessible route from the site arrival point.
-No other mention of any accessible requirements is made in 305.9, so does everything not mentioned in 305.9 get a pass? (maneuvering clearances and kitchenettes specifically)
Ch. 5, prescriptive-IEBC 507.1 pretty much waives all of the requirements of ch. 5 (which includes 506 on C of O's) unless deemed to be a life-safety hazard, except for structural unless the CBO waives those.
Ch. 6-12 are required to be used when using the work area compliance method. 607.2 directs that "the code" applies unless waived by ch. 12. By "the code" I assume it refers to ch. 6 through 12. IEBC 1204.1 tells us that the applicable provisions of ch. 10 apply (which pick up ch. 7,8,9) unless waived in 1204, but as discussed (without a clear consensus) ch. 10 doesn't apply...what now since 7,8,9 are triggered by ch. 10? If ch. 12 can be used regardless if ch. 10 can be used, then do we still use ch. 7 through 9 and ch. 12?
When I review things like this I start from a full IBC compliance perspective, then back out what doesn't apply in an existing building, then back out what wouldn't apply in an historical building. But, this is the first bona fide historical building I have actually reviewed as a C of O. When I back everything out, it would appear very little applies.
Has anyone else done a similar project?