If the Building Official and Fire Marshal disagree on occupant load, per your state statutes, how is this resolved?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
You are not answering the question. The FD and BD review the occupant load. If they disagree, how is that handled in your state?The RDP should be stating the occupant load and provide that on the code summary and life safety page. Also withe occupant count for each room with cumulative total for the exiting pathways and components tot he exterior. The BO then reviews and confirms.
Yes, same here.We talk, and we resolve such discrepancies (if they occur) by discussion and consensus
Yes, same here.
If there is no consensus, are there any laws, rules, etc, for resolution.
Naive questions:Our statutes don't offer a path to resolving a disagreement. The IBC says the Building Official shall establish the occupant load. The IFC says the Fire Marshal shall establish the occupant load.
Here where? Townships?Easy, no fire marshals or fire code here.
Here where? Townships?
In PA, many cities both small, medium and large have Fire Departments who enforce the NFPA standards adopted and sometimes the IFC which references many NFPA codes and standards. Reading, York, Wilkes-Barre, Scranton, Harrisburg, Allentown, Sharon, etc.
Some of these even have special fire districts within their city limits with even stricter rules and regulations such as no NM cable, no PVC conduit, and even more aggressive fire sprinkler requirements.
Yes and it is in the codes and the proper application of the 2 codes. If you did not adopt Chapter One then you might be SOLIf there is no consensus, are there any laws, rules, etc, for resolution.
Yes and it is in the codes and the proper application of the 2 codes. If you did not adopt Chapter One then you might be SOL
2018 editions
The IFC is not a construction code for buildings. It has requirements for specific uses and systems/equipment within a new building.specifically for new construction.
The IFC is not a construction code for buildings. It has requirements for specific uses and systems/equipment within a new building.
102.1 Application. This part of the code shall apply to all buildings, structures, or portions thereof, or facilities, for which application for an initial building permit was made on or after January 1, 2006, as outlined below, except as specifically provided for in the wording of a section.
[BE] 1004.1 Design Occupant Load. In determining means of egress requirements, the number of occupants for whom means of egress facilities are provided shall be determined in accordance with this section.
The most restrictive is used.If the Building Official and Fire Marshal disagree on occupant load, per your state statutes, how is this resolved?
You are not answering the question. The FD and BD review the occupant load. If they disagree, how is that handled in your state?
And Vice-VersusThe Building Official has the say, if the fire official is aggrieved they can appeal to the Building Code Appeals Board
Our state board says the building code is the starting document and the fire code is a reference document. Also the building official is the final judge on any code interpretation.If the Building Official and Fire Marshal disagree on occupant load, per your state statutes, how is this resolved?