I think pretty much everything is included in the egress system:but what if it does not land on the path of egress?
Then, more specifically as Yankee Chronicler mentioned:2018 IBC Chapter 2 Definition of “Exit Access”
That portion of a mens of egress system that leads from any occupied portion of a building or structure to n exit.
It's on an aisle accessway.
Thank you, I wasn’t implying anything was deficient, just wondering.That's usually how we do it unless its in nyc, 5% of the total number of seats.
The table has to be a certain height and the wheelchair needs to fit under the table, 19 inches. a lot of the times there is an accessible sticker on them. usually two legs instead of one on the table. We sometimes get existing conditions that don't meet accessible requirementsThank you, I wasn’t implying anything was deficient, just wondering.
I have never seen anything in a restaurant that looked like a “designated” wheelchair space. I always assumed that the hostess would pick an open table and remove a chair or two to make room for the wheelchair then put the chairs back after they leave.
Again, thank you, I wouldn’t be surprised to start noticing the stickers now.The table has to be a certain height and the wheelchair needs to fit under the table, 19 inches. a lot of the times there is an accessible sticker on them. usually two legs instead of one on the table. We sometimes get existing conditions that don't meet accessible requirements
keeping the path of travel at 36" clear (from face of floor trim base boards) to the designated percent of accessible tables is required. Providing a seamless entry and exit passage 36" wide is required including the clear floor approach spaces to doors, signage, and accessible floor transitions.We usually try to get 36" from the back of a wheelchair to any obstruction.
I understand that if its on the path of egress, but what if it does not land on the path of egress?
Would this still require 36" from this stool that's on the long table to the back of the wheelchair?
I think if the venue had more seats it would be 42” per 1029.1:keeping the path of travel at 36" clear (from face of floor trim base boards) to the designated percent of accessible tables is required.
IBC 2018 1018.2 Aisles in Assembly Spaces
Aisles and aisle accessways serving a room or spaces used for assembly purposes shall comply with Section 1029.
IBC 2018 1029.9.1 Minimum Aisle Width
The minimum clear width for aisles shall comply with one of the following:
4. 42” for level or ramped aisles having seating on both sides.
Exceptions:1. 36” where the aisle serves less than 50 seats.5. 36” for level or ramped aisle having seating on only one side.
That's for aisles, which are different from aisle access ways. If it's just an aisle access way it's my interpretation you just need enough space for a t-turn and of course a 36" wide aisle access way, usually much more than otherwise the minimum. Unlike aisles, a wheelchair space may overlap an aisle access way. Just as a person with no mobility impairment may have to stand to allow a person to pass in a row of seats, a person in a wheelchair may need to move a few inches.I think if the venue had more seats it would be 42” per 1029.1:
So this would be considered an aisle access way & not an aisle? you would not need 36" from the back of the wheelchair to the adjacent seat? If that's the case I've have been wrong about this.That's for aisles, which are different from aisle access ways. If it's just an aisle access way it's my interpretation you just need enough space for a t-turn and of course a 36" wide aisle access way, usually much more than otherwise the minimum. Unlike aisles, a wheelchair space may overlap an aisle access way. Just as a person with no mobility impairment may have to stand to allow a person to pass in a row of seats, a person in a wheelchair may need to move a few inches.
No worries as far as I’m concerned.Sorry to bring this old post up again
That’s a tough call in my opinion. I think I would consider connecting the exit doors with a single path through the spaces between the seating elements, this would be the aisle, then anything branching off that path would be an aisle accessway. But that’s where the “fun” starts - you draw one path that you think is the aisle and someone else could think it should be a different path. Your plan is tough because the widths are relatively close in size, so there's not really a major “thoroughfare” with “side streets” coming off of that. My suggestion to connect the exits with a path is an effort to find the major thoroughfare.So this would be considered an aisle access way & not an aisle?
From 2018 IBC Illustrated Handbook Comments on 1018.1 General
It is important to realize that the first element of any means of egress system is typically an aisle accessway, which then leads to an aisle. The code regulates aisle accessways to some degree in Group M occupancies, as well as in assembly spaces per Section 1029 but is silent for all other occupancy classifications. The building official must determine at what point an aisle accessway becomes an aisle and must be regulated for minimum width in accordance with this section.
Per A117.1 304.3.2 (T-Shaped Space) we’d need 36” for the arm across the top of T-shape if we use the knee space under the base of the T (highlighted in red in the image) - if there’s that much room under the table - so the 36” wide dimension you mention provides for the arm.If it's just an aisle access way it's my interpretation you just need enough space for a t-turn and of course a 36" wide aisle access way
Perhaps we are to assume they can use up to half of the depth of the table?keep in mind you have knee and toe clearance of about 19” depth underneath the dining surface
Yes, correct, the 2009 version. And thank you for the reminder to switch to the current edition, it’s been on my to-do list a while along with getting the 2021 IBC, I have lots of excuses why I keep putting that off and all of them stink!I think that's 2009 edition, right? May want to use 2017.
Not sure if this gets you there?Yes, correct, the 2009 version. And thank you for the reminder to switch to the current edition, it’s been on my to-do list a while along with getting the 2021 IBC, I have lots of excuses why I keep putting that off and all of them stink!
I was told to do that by my boss many years ago. I always thought it was for people to go behind the wheelchair. It's starting to sound like I have been doing this wrong all of these years. We always showed this on our drawings. I did not know about the difference between an aisle accessway & an aisle before today.Why are you measuring the min. 36” clear from back of wheelchair instead of tabletop?
If others in the restaurant have an alternate aisle route to get to their seats without having to go behind the wheelchair space, then why not measure between edge of tabletop to opposite obstruction (wall, fixed seat, etc.)?
When you measure from the edge of the table, keep in mind you have knee and toe clearance of about 19” depth underneath the dining surface, so that already makes the wheelchair space about 55” deep total.
2009 is still the code in many or most jurisdictions. Also 2017 is not yet a safe harbor.Yes, correct, the 2009 version. And thank you for the reminder to switch to the current edition