Not here. Out of hundreds of hot tubs I inspected i only ever saw 2 storable hot tubs.A typical hot tub is "storable" and thus not subject to 680.23. Part III of Article 680 vs Part II of Article 680.
Cheers, Wayne
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Not here. Out of hundreds of hot tubs I inspected i only ever saw 2 storable hot tubs.A typical hot tub is "storable" and thus not subject to 680.23. Part III of Article 680 vs Part II of Article 680.
Cheers, Wayne
Are you using "hot tub" as being distinct from "spa"? The typical "spa" I'm familiar with has "nonmetallic, molded polymeric walls" and thus meets the 2020 NEC Article 680 definition of being "storable".Not here. Out of hundreds of hot tubs I inspected i only ever saw 2 storable hot tubs.
The definition in the IRC for a hot tub or a spa is the same:Are you using "hot tub" as being distinct from "spa"? The typical "spa" I'm familiar with has "nonmetallic, molded polymeric walls" and thus meets the 2020 NEC Article 680 definition of being "storable".
Cheers, Wayne
OK, then 2020 NEC Article 680 also defines what it means for a spa or hot tub to be storable (emphasis mine):The definition in the IRC for a hot tub or a spa is the same:
Take II:Does it have a luminaire? 680.23
Or wet and outside and underground is a wet locationLooks like it depends on which code you are on or if it goes through a corrosive environment.
If it is 5' away, is it automatically not in a corrosive environment?
?If it is 5' away, is it automatically not in a corrosive environment?
noLooks like it depends on which code you are on or if it goes through a corrosive environment.
If it is 5' away, is it automatically not in a corrosive environment?
Correct....then we are back to whether or not the disco and therefore the feeders are in the corrosive environment or in the case of 2023, a wet location which would likely only get a pass if the disco was mounted on the exterior wall of the dwelling, but some people will argue that as well...Take II:
As this section applies to branch-circuit wiring (the title of 680.23(F)), if the disconnect in the OP contains OCPD, the supply to it is a feeder, not a branch circuit.
Thus the requirements of 680.23(F) do not apply to the supply side of that disconnect.
Cheers, Wayne