I'm at a loss and can't find anything governing perimeter fencing at a multi-family property and the number of pedestrian access gates required? Am I blind? Does it exist?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
Not that I am aware of.Does it exist?
Thank you - so the number of gates would be determined by the city?Not that I am aware of.
I appreciate this.2022 CBC
1004.7 Outdoor areas. Yards, patios, occupied roofs, courts and similar outdoor areas accessible to and usable by the building occupants shall be provided with means of egress as required by this chapter. The occupant load of such outdoor areas shall be assigned by the building official in accordance with the anticipated use. Where outdoor areas are to be used by persons in addition to the occupants of the building, and the path of egress travel from the outdoor areas passes through the building, means of egress requirements for the building shall be based on the sum of the occupant loads of the building plus the outdoor areas.
Exceptions:
1. Outdoor areas used exclusively for service of the building need only have one means of egress.
2. Both outdoor areas associated with Group R-3 and individual dwelling units of Group R-2.
If you're talking about an existing building though, it would only have to comply with the codes in effect at the time it was built.
I read through this and it would be applicable to what I am dealing with. There is nothing definitive about the number of gates in the perimeter fencing. I assume this would be determined by the local building department?2022 CBC
1004.7 Outdoor areas. Yards, patios, occupied roofs, courts and similar outdoor areas accessible to and usable by the building occupants shall be provided with means of egress as required by this chapter. The occupant load of such outdoor areas shall be assigned by the building official in accordance with the anticipated use. Where outdoor areas are to be used by persons in addition to the occupants of the building, and the path of egress travel from the outdoor areas passes through the building, means of egress requirements for the building shall be based on the sum of the occupant loads of the building plus the outdoor areas.
Exceptions:
1. Outdoor areas used exclusively for service of the building need only have one means of egress.
2. Both outdoor areas associated with Group R-3 and individual dwelling units of Group R-2.
If you're talking about an existing building though, it would only have to comply with the codes in effect at the time it was built.
It depends entirely on the situation. If you're talking about new construction, then it would be the responsibility of the designer (hopefully an Architect) to determine the size and number of exits (along with everything else), then the local building department would be responsible for reviewing the plans for code compliance.I read through this and it would be applicable to what I am dealing with. There is nothing definitive about the number of gates in the perimeter fencing. I assume this would be determined by the local building department?
I'm at a loss and can't find anything governing perimeter fencing at a multi-family property and the number of pedestrian access gates required? Am I blind? Does it exist?
Have no clue what "frontage Increase" is?Don't forget about the frontage increase if it is required in a new or existing building. The fence could be in the way.
"Pedestrian access" could be ingress or egress.The original question asked about pedestrian access (i.e. ingress) gates. The building code doesn't address the number or size in INgress routes, for buildings or for fenced yards or courts.
Steveray cited IBC section 1028.5, which regulates egress. Egress is regulated by the building code, so a proper answer will be based on egress, not ingress, and will have to take into account the occupant load of the building and the number and arrangement of exit discharge routes.
It is the open space required around a building. It is part of the calculations needed when determining the allowable size of a building.Have no clue what "frontage Increase" is?
The original post was somewhat of a hypothetical:You are assuming, the use of "area Increase" for the project?
I did not and still do not think, it was hypothetical.The original post was somewhat of a hypothetical:
1. Does the code require perimeter fencing on multifamily properties?
2. When #1 is "yes", when/where does the fencing need (pedestrian) gates?
So I think most of the responses at this point are just brainstorming the various scenarios under which such things might occur. We are all exploring various assumptions, for the sake of discussion.