Without comment on what the building code requires or allows, from a purely risk point of view, _if_ you knew that fire risk and wind/seismic risk were independent, it would be reasonable to take the attitude that you don't need to guard against both happening simultaneously, as that would be very unlikely. So if the unit with the shear wall burned down, the strategy would be to repair the other unit before the next wind/seismic event.So what happens if the unit in which you install the plywood shear wall burns down? The other unit now has no shear resistance on that line.
Without comment on what the building code requires or allows, from a purely risk point of view, _if_ you knew that fire risk and wind/seismic risk were independent, it would be reasonable to take the attitude that you don't need to guard against both happening simultaneously, as that would be very unlikely. So if the unit with the shear wall burned down, the strategy would be to repair the other unit before the next wind/seismic event.
But I expect that wind/seismic risk are in fact correlated, so that be a bad strategy. E.g. an earthquake causes a fire that burns down one side; the other side survives the fire but is damaged by an aftershock due to loss of the braced wall line.
Cheers, Wayne
Shirley I could find a way to make it work.....I would assume sheathing on both wood walls?
I would be fine with it, it is pretty clear that what you have will do the job, given the way the wall is designed in the UL assembly with an exposed side and a non-exposed side, and you basically have two of these walls face-to-face. The plywood is on the non-exposed side, so I think it's no different than using whatever you want on the the top side of a floor system.
Also note that the townhouse units do not have to be structurally independent if you are using a 2 hour common wall per 2021 IRC R302.2.6, Item 5, which references R302.2.2, Item 2.
You should get clarification where he is specifically calling for the sheathing to be installed. Hopefully Exception 1 would be applicable for your project.I meant as opposed to in between the two studs walls,
Yes, but the way the wall is tested in this particular system, the shaftwall in the middle is counted as your first layer of defense. If you look at the system attached, it's meant to be a one-way system.Both sides of a townhouse party wall are exposed sides.
Yes, but the way the wall is tested in this particular system, the shaftwall in the middle is counted as your first layer of defense. If you look at the system attached, it's meant to be a one-way system.
If you were in a building designed as above, and and the wall runs east to west, if there was a fire on the north side, it would have to burn through the north piece of plywood before it encountered the first tested part of the fire rated assembly, and the plywood on the south side would be on the non-exposed side.
My point is that the plywood on the side the fire starts on is not really part of the assembly designed to stop the fire from that direction. If anything, it makes the wall more fire-resistant because it should add at least a few minutes of calculated resistance. Plywood vs drywall on either side is likely irrelevant.
None of this is accurate. The entire assembly provides the fire resistance. There are no exceptions in U336 for elec boxes beyond those in the gen notes for all wall assemblies.The gypsum shaftwall is the part that provides the fire resistance. That's why in these assemblies there is no need to use putty packs or rated boxes where electric receptacles penetrate the membrane.
The problem is they allude to the shaftwall being it's own wall, but they show the wood because that is how they tested it....
View attachment 14326
The problem is they allude to the shaftwall being it's own wall, but they show the wood because that is how they tested it....
View attachment 14326
I trust the engineer is competent enough to know burn clips don't have a tested shear capacity.That's because it won't stand up without the stud wall on at least one side.
But I still think we need to know if the OP was asking about plywood on only one side, or plywood on both sides.
Yes, but the sheathing is shown opposite the burn clips so it would just get the shear of a "one sided" assembly...Like an unfinished garage or barn type building...I think yankee was referring to both wood walls being "shear rated" which may or may not actually be required....I think you are in agreement with that with your reference to the shear of the clips, but it was unclear. We don't generally get engineers on IRC structures....I trust the engineer is competent enough to know burn clips don't have a tested shear capacity.