Requirements for emergency egress from gated complexes?

ArthurPeabody

REGISTERED
Joined
May 17, 2022
Messages
4
Location
albuquerque
My condominium complex recently added fences with gates. We now have only 1 automated gate for automobiles that opens (the other 3 are permanently locked) and all 4 pedestrian gates are permanently locked (because people were propping them open.) The automated gate works with a Bluetooth app; the pedestrian gates have keyboards to take unlocking codes to enter. We have 167 units, at least 200 residents. This seems unsafe. I can't find the requirements for this in the code. Do any of you-all know? Thanks.
 
Is a code required to open the gates from the inside? How about the car gate? I don’t think a Bluetooth app is a great way to go unless there is also a keypad option. All of this will provide a false sense of security.
 
Is a code required to open the gates from the inside? How about the car gate? I don’t think a Bluetooth app is a great way to go unless there is also a keypad option. All of this will provide a false sense of security.
The only gate that can open at all is the car gate. It opens automatically when a car wants to leave from the inside, but doesn't sense people for that purpose. You may not care for Bluetooth but the only argument I can make that will sway the board will be one that cites code.
 
The only gate that can open at all is the car gate. It opens automatically when a car wants to leave from the inside, but doesn't sense people for that purpose. You may not care for Bluetooth but the only argument I can make that will sway the board will be one that cites code.
Sorry but I have no answers for you. There's lots of people here at the forum so perhaps answers are not far away.

I can't enable the Bluetooth on my S10 Galaxy phone while in my Tundra. The two will not talk to each other and the phone keeps whining about it. So I turn off the Bluetooth on the phone. Of course I have a button on the mirror to open my garage door so the Bluetooth is not important unless I want to make a phone call through the truck speakers....and I don't. My GMC had it's own phone number so I could always call from the truck....and never did.

The pedestrian gates should be able to open from the inside without use of a keypad code, Bluetooth app or key....but since this is not the egress door from a dwelling, I can't think of a code that would back that up.
 
Last edited:
Is there enough interior room to be considered a "dispersal area"?

[BE] 1028.5 Access to a public way. The exit discharge shall provide a direct and unobstructed access to a public way .
Exception: Where access to a public way cannot be provided, a safe dispersal area shall be provided where all of the following are met:
1. The area shall be of a size to accommodate not less than 5 square feet (0.46 m2) for each person.
2. The area shall be located on the same lot not less than 50 feet (15 240 mm) away from the building requiring egress.
3. The area shall be permanently maintained and identified as a safe dispersal area.
4. The area shall be provided with a safe and unobstructed path of travel from the building.
 
That was a quick "No"...........can you provide a sight plan?

It was quick because I had already read that section of the code in search of something relevant to my situation.

It was easy to make because there is no interior space. All the units open only to the outside, the only inside space other than residences is a small office and laundromat, nowhere near enough for everybody and part of the buildings to boot. The only place to run is outside.

I have no site plan, but it's not complicated: 4 buildings separated by north/south driveways, a parking lot on the south side, an exit on the west side. All 3 north/south driveways used to be open; now they're all permanently closed. Only the west side has an exit, and that onto a street that dead-ends on the south side, so there's only 1 way for an automobile to get out.

Only a reference to code or law will make any difference. I watched a large apartment building burn some 45 years ago. I can imagine what would happen here, when 150 cars and 200 people all try to exit through 1 gate. I wouldn't even look at the code if it were my decision. At least all the pedestrian gates should open.
 
Don't recall if it was a code thing, but a site of four mid-rise apartment buildings I used to manage in Baltimore had fenced/gated patios adjacent to them. They all had a handicap accessible push button to activate the gate (far enough away that someone outside the fence couldn't poke it).

If it was code related, it was probably the dispersal area requirements. Smallest building was about 75-80 units and at max occupancy, there certainly wasn't 5 sq feet per person on the patios.
 
1010.2 Gates
Gates serving the means of egress system shall comply with the requirements of this section. Gates used as a component in a means of egress shall conform to the applicable requirements for doors.

MEANS OF EGRESS. A continuous and unobstructed path of vertical and horizontal egress travel from any occupied portion of a building or structure to a public way. A means of egress consists of three separate and distinct parts: the exit access, the exit and the exit discharge.

1010.1.9.9 Sensor Release of Electrically Locked Egress Doors
Sensor release of electric locking systems shall be permitted on doors located in the means of egress in any occupancy except Group H where installed and operated in accordance with all of the following criteria:
  1. The sensor shall be installed on the egress side, arranged to detect an occupant approaching the doors, and shall cause the electric locking system to unlock.
  2. The electric locks shall be arranged to unlock by a signal from or loss of power to the sensor.
  3. Loss of power to the lock or locking system shall automatically unlock the electric locks.
  4. The doors shall be arranged to unlock from a manual unlocking device located 40 inches to 48 inches (1016 mm to 1219 mm) vertically above the floor and within 5 feet (1524 mm) of the secured doors. Ready access shall be provided to the manual unlocking device and the device shall be clearly identified by a sign that reads "PUSH TO EXIT." When operated, the manual unlocking device shall result in direct interruption of power to the electric lock—independent of other electronics—and the electric lock shall remain unlocked for not less than 30 seconds.
  5. Activation of the building fire alarm system, where provided, shall automatically unlock the electric lock, and the electric lock shall remain unlocked until the fire alarm system has been reset.
  6. Activation of the building automatic sprinkler system or fire detection system, where provided, shall automatically unlock the electric lock. The electric lock shall remain unlocked until the fire alarm system has been reset.
  7. The door locking system units shall be listed in accordance with UL 294.
1010.1.9.10 Door Hardware Release of Electrically Locked Egress Doors
Door hardware release of electric locking systems shall be permitted on doors in the means of egress in any occupancy except Group H where installed and operated in accordance with all of the following:
  1. The door hardware that is affixed to the door leaf has an obvious method of operation that is readily operated under all lighting conditions.
  2. The door hardware is capable of being operated with one hand and shall comply with Section 1010.1.9.6.
  3. Operation of the door hardware directly interrupts the power to the electric lock and unlocks the door immediately.
  4. Loss of power to the electric locking system automatically unlocks the door.
  5. Where panic or fire exit hardware is required by Section 1010.1.10, operation of the panic or fire exit hardware also releases the electric lock.
  6. The locking system units shall be listed in accordance with UL 294
 
  • Like
Reactions: ICE
It was easy to make because there is no interior space. All the units open only to the outside, the only inside space other than residences is a small office and laundromat, nowhere near enough for everybody and part of the buildings to boot. The only place to run is outside.
"Is there enough interior room to be considered a "dispersal area"?"

When fatboy said "interior" he meant on the same lot....not inside a building.
 
It sounds like the complex is large enough that when exiting the buildings you are in areas meeting the exit discharge requirements and the fence and gates you are talking about are well away from the buildings not inhibiting a compliant refuge area in an emergency. And what you are asking about might be secondary gates, that provided a simpler way to get out of the complex, that were closed off in leu of high security measures.

Thus, the reason most posters are asking for a sight plan, is without knowing all the correct and pertinent information that a sight plan will have, no one can really give you a code section for your question, only speculating.

if this complex sits in the middle of NYC, downtown Albuquerque or 500 acers in NM is context one needs to answer the questions

Context is everything, and though you might think you have provided enough, based of your OP and continued posts, there are about 3 different sight plans that come to mind, all with different answers.
 
Find out if they ever got a permit for the fence and gates. If they did it probably passes code. If they did not get a permit they should be fined.
Rick,

A permit being issued or not, might be a requirement in your state and AHJ.

However, many states, especially in the mid and southwest, I have been shocked to hear that none are required, but to say was a permit issued yes/no is only one course of question, one might not even have been required, nor even close to being a fine.
 
It's Eagle's Nest at 2800 Vail Ave SE in Albuquerque. I hate the premises egress (and ingress) situation here, its cumbersome to me and seems potentially dangerous too.

Lots of things could impede leaving in a hurry, just off the top of my head: dead phone battery, broken phone, one or more of the following inoperable on phone: bluetooth, gps, mobile data, the app (all four must work in order to exit), the exit (which is the only one) is blocked, any one part of this crappy gate stops working, my car won't run (sensor doesn't work for pedestrians!), ad infinitum.

Sometimes I run, go for a walk, or walk to the store and have to either bring my phone (dislike on a run), hop the fence (stabbed my hand the other day doing this cause its got spikes on top, like everywhere in Abq cause of property theft), or there's one spot I can crawl under it on my back.

Lots of reasons I might want or need to leave without either my phone or car from this place, but it's like a frinking prison if you don't have all that stuff working and immediately at hand.

Looks like the premises is on 10k sqft. If the buildings took up more than half, which I doubt, there would still be ~20 sqft per person, more than enough for a 'dispersal area'. Nevertheless, the situation is very strange to me and a red flag. People are not free to easily leave this spot. I am abled, and if need be I'm outta here in under a minute, but most are not able or willing to jump an 8' fence with spikes. Nor should that be expected of them. Essentially, we cannot leave on foot (without an operable smartphone).
 
Last edited:
It's Eagle's Nest at 2800 Vail Ave SE in Albuquerque. I hate the premises egress (and ingress) situation here, its cumbersome to me and seems potentially dangerous too.
I'm familiar with that area, and yes security-wise it's a tough part of town. The old Google street view photos show at least 2 pedestrian gates, both of which are closed with a chain and padlock. Don't know if the fence system has changed over the years.

1733269387682.png

If this were new construction that was proposing no pedestrian gates, then per IBC 1028.5 (exception), you would need a "safe dispersal area" sized for at least 5 SF per person and located at least 50' away from the building that is being egressed. The aerial view shows lots of dispersal space available.

I don't know when this was first built, but if it was after 1991 they would be subject to the Fair Housing Act and would need to provide an accessible pedestrian/wheelchair path that connects to the public right of way (for residents who don't drive). If you are really concerned about safe exiting, you can call the city code enforcement department and ask them if that fence was legally permitted and if it is allowed to have no pedestrian access/egress.
 
I'm familiar with that area, and yes security-wise it's a tough part of town. The old Google street view photos show at least 2 pedestrian gates, both of which are closed with a chain and padlock. Don't know if the fence system has changed over the years.

View attachment 14780

If this were new construction that was proposing no pedestrian gates, then per IBC 1028.5 (exception), you would need a "safe dispersal area" sized for at least 5 SF per person and located at least 50' away from the building that is being egressed. The aerial view shows lots of dispersal space available.

I don't know when this was first built, but if it was after 1991 they would be subject to the Fair Housing Act and would need to provide an accessible pedestrian/wheelchair path that connects to the public right of way (for residents who don't drive). If you are really concerned about safe exiting, you can call the city code enforcement department and ask them if that fence was legally permitted and if it is allowed to have no pedestrian access/egress.
Hey, I appreciate your input.

I guess it meets the safe dispersal area requirements and was built in '74, so it is what it is. The fences are unchanged, including chain and padlocks on the pedestrian doors.

For me personally it's just that my life of ultra-convenience is slightly less-so due to this, aka I'll be fine. On the wrong day maybe it would be an issue for the wheelchair bound person I've seen get dropped off a couple times from a city transportation van. No one asked me to get all Karen on their behalf, however, and if everything's up to code then I'll leave it be; will continue to travel over and under the fence time to time, though, cause I refuse to be forced to have my phone on my person every living moment of my life.
 
Hey, I appreciate your input.

I guess it meets the safe dispersal area requirements and was built in '74, so it is what it is. The fences are unchanged, including chain and padlocks on the pedestrian doors.
The fences have definitely changed since time of first construction. Over on Columbia Drive, there used to be a walkway that connected to the public sidewalk:
1733277258460.png

By 2022, they added a fence and padlocked that shut:
1733277370371.png

The gate was designed with lever entrance hardware, as if it was intended to be for entry:
1733277485181.png
So it might be worth investigating if this work was done under permit.

But be careful what you wish for. I've seen the police reports and statistics for unsecured developments located not too far from there, and it isn't pretty. You may find yourself grateful for the security this fence provides, as long as you know how to find safe dispersal in event of a fire.
 