I assume you are referring to the CBC.
You also have to consider the allowable height in terms of the number of stories per Table 504.4. Group A-3 is limited to 3 stories without an area increase and 2 stories with an area increase. Thus, you cannot use the nonseparated occupancies method to determine your allowable area. However, Group R-2 occupancies can be four stories with or without an area increase since your building is under 60 feet in height.
Thus, you will need to separate the Group A-3 occupancy on the first story from the second story with a 1-hour horizontal assembly as an occupancy separation per Table 508.4 (which you have to do anyway for dwelling unit separation per Section 420). Since the Group A-3 occupancy does not exceed the allowable height in stories, you can use the "without height increase" allowable areas in Table 506.2, but now you have to determine your allowable area based on separated occupancies per Section 508.4.
I used separated method. I used without height increase area but the plan checker said that I should use area 11500. I don't know if he is using 'NS' or 'SM with area increase'. I don't understand his comment. I also have other occupancy in the first floor. He said to use SM in other occupancies. Below is his whole comment. the building is 4 story. A-3 only allow 2 or 3 story. Does "without height increase" include story increase? A-3 is only in the first floor.
"The sprinkler increase provisions must be viewed for the entire building. Since this Type VA
building is four stories in height, the sprinkler system shall be used to increase the
allowable height and number of stories. The allowance to use the sprinkler system for the
area increase in addition to the height and story increase is limited to an individual Group
R-2 occupancy and cannot be used for the allowable area increase for any other
occupancies in this building, even if an occupancy is only a single story. At Group A-2/A-3
occupancy, please revise the tabular allowable area to be 11,500 square feet. Sheet A0.50.
CBC Table 506.2 footnote k
2
nd Review Comment: This issue has been addressed. However, it is unclear from review
of the newly revised allowable area calculation how Groups S-2 and M occupancies have
been accounted in the area ratio calculations and why the Group S-2 parking garage has
been reclassified as a nonseparated Group B occupancy. Furthermore, since the building is
four stories in height, the allowable area ratio calculation for Groups S-2, M and B
Occupancies shall be based on the SM (not S1) tabular values. Sheets A0.50, A0.61,
A0.71. CBC Sections 506.2.3, 506.2.4 "