Does a detached accessory structure, such as a garage, require a man door, or is the overhead door sufficient?
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I posted this in the Residential Building Code section.Residential (IRC) or commercial (IBC)? If IBC, how large/what's the occupant load. Overhead doors are allowed as egress under the IBC if serving (if I recall correctly) either 10 or less, or under 10 occupants.
Other doors shall not be
required to comply with these minimum dimensions. Egress
doors shall be readily openable from inside the dwelling without
the use of a key or special knowledge or effort.
Let's see if everyone agrees on this.It doesn't appear that other door are regulated, so I'm going to go with all you need is the overhead garage doors.
And if the power fails?Much easier to use extra remotes from house to open or close the overhead doors
I searched for this issue because I was certain it had been discussed and the simple and least expensive option for power failure is a battery backup.And if the power fails?
or
I searched for this issue because I was certain it had been discussed and the simple and least expensive option for power failure is a battery backup.
Is this much different as fast as egress than self storage bays with just an overhead door?
The least expensive would be reusing the existing opener when replacing the old garage doors. But of course, California will not allow that and the garage door companies will not reinstall the old opener because a battery backup is required. That came about after an elderly couple was found deceased in the car that was in the garage after the Camp fire. They made no attempt to take out the door with the car. So now we all have a battery next to the ceiling. I used mine recently when the power was out for twenty hours.least expensive option for power failure is a battery backup.
As for the accessory building, I think once the square footage is 1000 SF it becomes a structure that needs a man door.
I recall the 1000 sq.ft. limit so I went looking for it but alas, I can't find it. It might be with the gate key to our back yard as I can't find that either.Code citation?
I recall the 1000 sq.ft. limit so I went looking for it but alas, I can't find it. It might be with the gate key to our back yard as I can't find that either.
CBC/IBC 1010.1.2 Egress Door Types
Egress doors shall be of the side-hinged swinging door, pivoted door, or balanced door types.
Exceptions:
1. Private garages, office areas, factory and storage areas with an occupant load of 10 or less.
Per table 1004.5, the occupant load for a parking garage is 200 SF/occ. That’s about 10’x20’, the size of a single parking space inside a garage in a typical residential zoning code.
2 cars x 3 rows is approx 40’ deep x 30’ wide, 1200 SF, which is 6 occupants.
A garage of 2000 SF in area would qualify as “10 occupants or less”, at which point an egress door is not required to be swinging.
You would also need to check to see if accessibility codes would apply to your proposed use.
What recall was a limit on the size of a garage of 1000 sq.ft. It had nothing to do with occupant load.
I hear you, but R311.2 only addresses dwelling unit doors. So here in California either you conclude that the IRC / CRC has no minimum egress door requirements for accessory structures/uses to residential dwellings, or you go back to chapter 1 of the IRC to see if it defers to the IBC / CBC for scoping.But this question isn't an IBC question. It's an IRC question.
Given the inclusion of "structures accessory thereto" in IRC/CRC 1.1.3's scope, isn't that the only possible conclusion?I hear you, but R311.2 only addresses dwelling unit doors. So here in California either you conclude that the IRC / CRC has no minimum egress door requirements for accessory structures/uses to residential dwellings
Given the inclusion of "structures accessory thereto" in IRC/CRC 1.1.3's scope, isn't that the only possible conclusion?
Cheers, Wayne
Hypothetical: A 1,000 SF house with an attached 20,000 SF garage that holds a private car collection. Does the IRC require any occupant means of egress for the garage at all? (For that matter, does the unamended IRC have any limitations as to the allowable area of either the residence or its accessory uses other than height?)Given the inclusion of "structures accessory thereto" in IRC/CRC 1.1.3's scope, isn't that the only possible conclusion?
Cheers, Wayne
Sure, you can refer to IBC/CBC Chapter 3 to decide based on the use if there are in fact multiple occupancies or not. I'm not so versant with that Chapter, but I imagine your outlier examples would depend on whether the building is used just by the owner and their family, in which case it would be accessory to the one family dwelling and under the IRC. Or whether it is, say, open to the public for tours, in which case it might be a different occupancy which is subject to the IBC.In my opinion California modified the IRC via 1.1.3.1 (see post #20) to refer us to the CBC as the primary/ precedent scoping document when dealing with multiple occupancies.