jar546
CBO
What are your thoughts on this? This is an absolute violation in my opinion. The framing was existing, the new foam insulation against the roof deck and masonry chimney are new.
Your premier resource for building code knowledge.
This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.
Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.
Ready to upgrade? Log in and upgrade now.
I doubt it but the contractor will have to find out and report it.Is the flue listed for direct contact?
Yes, agree. Waiting on the contractor to prove whether or not the exception applies. There is nothing visible that would lead me to believe it is lined with anything other than a typical flue from the 1960's.There are a couple exceptions and I guess they could possibly line it...
R1003.18
Any portion of a masonry chimney located in the interior of the building or within the exterior wall of the building shall have a minimum airspace clearance to combustibles of 2 inches (51 mm). Chimneys located entirely outside the exterior walls of the building, including chimneys that pass through the soffit or cornice, shall have a minimum airspace clearance of 1 inch (25 mm). The airspace shall not be filled, except to provide fire blocking in accordance with Section R1003.19.
Exceptions:
- 1.Masonry chimneys equipped with a chimney lining system listed and labeled for use in chimneys in contact with combustibles in accordance with UL 1777 and installed in accordance with the manufacturer’s instructions are permitted to have combustible material in contact with their exterior surfaces.