Given:
Storm shelter is being required for an existing daycare.
Storm shelter will have an accessible restroom.
Question:
While calculating the occupant load, does the area within the restroom stall count? Or does the area of the restroom need to be excluded from the available shelter area?
Please don't ask me to ask the plan reviewer. Her typical answer is often "... everything needs to be per code ..." until we go a few rounds of review and figure things out.
As always, thanks in advance.
ICC Certified Plan Reviewer
NFPA Certified Fire Plan Examiner
The usable floor area does not get to include occupant support areas, which includes toilet rooms. However specific to a tornado shelter (shorter duration usage) then if a multi-stall toilet room is included the toilet are other than the stalls or other private areas can be used. If single user toilet rooms then the entire toilet room can be considered. 2020 ICC 500 section 502.
Looks like I need to reduce my gross square footage by 15 percent for the classroom with movable furniture.
Technically speaking, I need to remove the walls around the restroom (making the entire storm shelter a restroom) or subtract the yellow restroom.
You are very helpful Sifu.
Just happened to review one last week, so it was fresh in my mind.
So would you extend the yellow area for the restroom to cover the lavatory and its floor clearance? Probably not enough area to make a difference.
Not related to occupant load, but your lavatory configuration made me think of this thread:
Here’s a video of the restroom from the TBCF YouTube channel:
606.2 under Lavatories and Sinks requires a clear floor space for a forward approach complying with 305.3. Neither sections require the lav to be centered with the sink. This would comply as long the trash can is completely not Infront of the lav.
First time I looked at the drawing. I think you need to account for one wheelchair space at 10sf, and reduce the area by one of the methods they list for the loose tables and chairs.
This reminds me of when I designed a RECESSED paper towel and trash combo. The drywallers did their thing and the contractor then used a surface-mounted combo. The inspector rejected it. The inspector rejected a few other picky ADA items also. We simply let the permit expire and everyone forgot about it.
Which should have meant no certificate of occupancy, and THAT would have meant that if the owner had moved in they were occupying the building illegally.
Which may not be an issue for years -- until something happens, and everybody lawyers up and the attorneys run around looking for someone to pin liability on.
Given:
Question:
If I'd seen it sooner, I would ask why use group you are using. It can be B, E or I depending on the specifics. I believe that adding a shower with an overnight capacity would make it an institutional use unless you are to separate the occupancies. And 1004.2 flip flops between net sf and gross sf depending on the occupancy. If I was just to go by the daycare calc of 35sf net, then I wouldn't count the bathrooms at all, just the classrooms and IMO I would subtract out all the built-in countertops, but not moveable furniture. But the plumbing code, to determine the number of fixtures, has its own calculations. As well as licensing requirements. I've done a few daycares and found them to be an incredible tangle of regulations.