AITA? Storage building exits
Inspector Gadget
New Brunswick
Had an application come in for an industrial building. >600m2 (>6000 ft2 for you murricans).
Canadian Code requires this floor are to have more than one exit (outward swinging door).
Designer pushing back, with the declaration the "actual" area will be far less because sand/salt will be stored in the structure, and it's low human occupancy.
Received the "We've done a dozen of these in the province, never had to do this anywhere else" line.
The way I see it, the floor area is clearly defined as outside wall to outside wall - independent of what's inside. The structure requires two exits. It exceeds the 200m2 limit under Part 3 for one exit, simple and easy.
Part 2, which deals with farm buildings (low human occupancy) has the same criteria, btw., so "low human occupancy" doesn't act as the get out of the second exit free card, even if used as a reference/alternative solution. (And it's not a farm building in any event.)
Thoughts?
Your view would be correct under the IBC and, assuming the Canadian Building Code has a similar definition for building area, you are correct and the designer is blowing smoke. The designer's view is a lot like saying that the "actual" area of an 80,000 square foot supermarket is really only 20,000 square feet because 60,000 square feet are occupied by shelves and products. That's not how this works.
"I've been doing it this way for thirty years."
"Then you've been doing it wrong for thirty years."
Not sure about Canadian code, but IBC1004.5 allows the building official to make a determination that the actual number of occupants in a space may be lower than determined by the occupant design load. In that instance the lower occupant load gets posted.
I used this often on basketball courts at private fitness centers. The normal occupant design load for a typical gym almost assumes a packed high school rally, whereas the actual fitness center use maybe tops out around 20 people per court (2 teams of 5 people each playing a half-court game).
Is there a similar discretionary provision in the Canadian code for something that is essentially raw material shelter?
For example, what is the occupant load of a grain silo?
Normally, I am a firm adherent to minimum safety code requirements. However, there are rare and reasonable circumstances where an inspector must point out a serious safety concern, even if it is not explicitly addressed in code. Courts in my jurisdiction have consistently held that the burden lies with the inspector/city to demonstrate that a condition presents a genuine health or safety hazard.
That said, in any commercial or industrial building, a secondary exit located at a significant distance from the main entrance should be considered a baseline safety expectation. For example, if a dump truck unloading salt or a forklift moving pallets were to catch fire near the main entrance, occupants could be trapped without a viable means of escape. Or in this day and age, a shooter situation, workers not trapped.
At a minimum, I believe the inspector should offer the builder to propose a simple secondary egress point of his choice —either a door or a window—sufficient to allow:
  1. Safe and rapid evacuation of occupants
  2. Access for emergency personnel
  3. should the primary entrance become compromised.
Giving the question to the builder, explaining the dilemma, giving him latitude to do it his way, should dismiss any pushback. " I am very uncomfortable with only one exit. Why don't you come up with a solution that allows someone trapped inside a second egress, or rescue another entrance and we will almost certainly go with it."
LOL, the logical fallacy Argumentum ad antiquitatem occurs when someone claims that something is right, correct, or better simply because it has "always been done that way" or has been done that way for a long time.
Canadian codes allow a different occupant load than what is calculated, provided it is posted. However, that would not have an impact on the two exit requirements. The number of exits is denoted by remoteness and travel distance requirements. Exit size (above the minimum door size) is driven by occupant load.
Yep..beating down the OL has nothing to do with it if OL is not the driving factor for the number of exits...
It sounds like law is a little different in Canada.
Case law in Canada has established that the code is the minimum standard in relation to what can safely be built. A building inspector only needs proof that the owner/contractor contravened the code.
A building designer can propose something that is demonstrated to be "just as safe" and it can be found to be acceptable by the AHJ. Furthermore, courts have found that failure to get a building permit and/or allow mandatory inspections results in a presumption that the building is unsafe.
Recently we had a city's building official's order was appealed. In my decision I found that the fact that the owner had not taken out a permit resulted in the presumption that the construction was unsafe (someone who is clearly flouting the building regulatory regime cannot be assumed to be compliant with other building regulatory requirements). This element (among others) was then appealed to an appeals court judge, who found that that "I did not make a mistake at law" with classifying the building as unsafe.
Thoughts?
Ask for code justification for a single exit.
Sounds like a whole lot of "Bullshit, Baffle, Belittle" style designing to me.
Assuming this is coming from another one of my employer's departments, many building departments have reported to me that when they see who the owner is, they don't actually do a code review and just issue the permit (even things like schools and hospitals). This is incorrect in accordance with Section 3 of the BCAA. They are subject to the same review and inspection process as everyone else. I have spent a lot of my time explaining to my colleagues that yes, they do need to follow the code and no, they don't get any exception.
I like this. Maybe a new BBB rating system is in order. Probably a lot more informative than the current BBB rating we have.
What constitutes your jurisdiction? Your state, or your county?
That view would very definitely not apply in my state. The building code (and in this state the State Building Code legally means the IBC, IRC, IPC, IMC, NEC, IEBC, IECC, ICC A1771.1, and several other documents specifically enumerated in the enacting legislation). The State Building Code is the legally binding minimum standard, so if the code says two means of egress and a designer or contractor only provides one means of egress -- we don't have to show why the code should apply, the perpetrator is deemed to be in violation. Period.
Assuming this is coming from another one of my employer's departments, many departments departments have reported to me that when they see who the owner is, they don't actually do a code review and just issue the permit (even things like schools and hospitals). This is incorrect in accordance with Section 3 of the BCAA. They are subject to the same review and inspection process as everyone else. I have spent a lot of my time explaining to my colleagues that yes, they do need to follow the code and no, they don't get any exception.
I'd heartily agree. I have seen more than a few provincial building alterations/new builds where the government didn't seem to think the Code applied to them. If I had a loonie for every time I've had the conversation that started with...
"We've never had to do that before ...."
In this case, the designer came back with a vastly better (and better documented) approach - essentially stating that the building was a low-human-occupancy structure not easily classified under 3.2.2, and more in line with the new Part 2 G4 occupancy. The argument (supported by an analysis made by a qualified fire protection specialist firm) makes sense - essentially the pitch was that LHO occupancies are allowed one exit under G4, and were this a farm occupancy, there would be no issue.
The irksome thing is that the letter they used was a couple of years old, and made reference to the future allowances under 2020 code, so they clearly *had* faced this kind of opposition from another AHJ before. That makes me inclined to believe that someone figured the country bumpkin would rubber-stamp the application without suitable review. Next we'll see if they have CAN/ULC S109 documentation for the structure's fabric.... that could be interesting.
Then we'll see if they read the plans review wherein I make note of the site plan showing a yet-designed building to be placed 8m away on the long edge of the tarp/tent structure, and raise the issue of "y'all may wanna do some spatial separation calcs before you wed yourself to this location."
What bothers me is the number of times I get the "we've never had to do that before" statement, and I don't get the feeling that other AHJ's have, in fact, done appropriate due diligence. I'm still relatively new to this biz .... I shouldn't be the one making these discoveries.
If the floor is used for storing salt and sand when the building is in use, do you include that floor space in calculating occupant load? I look in the highway department building a few miles away and there is sometimes barely room for anyone with all the salt dumped there before snow flies.
That was the designer's original argument. It's also not correct by definition.
Floor area means the space on any storey of a building between exterior walls and
required firewalls, including the space occupied by interior walls and partitions, but
not including exits, vertical service spaces, and their enclosing assemblies.
I ran into that with the protection of foam when I first started. No one was protecting foam in floor joist cavities (unfinished basement). And no one was protecting 1/2lb foam at all.
Why? Well, in joist cavities, the reason I got was that "it is not a significant enough hazard". What analytical methods did they use to come to this conclusion? No one could answer me. For 1/2lb foam the answer I got was the foam doesn't sustain a flame. When I asked what about the low flashpoint combustion gasses that get released as it does burn (from the wood framing all around it), and the resulting early flashover, all I got in response was blank stares.
Too many of us look for the easy answer of why I don't have to do something. Then when you do something that differs from the widely accepted looking in the other direction of the violation, your fellow inspectors try to undermine and exert influence to stop you (the above interaction earned me a reputation of being overly restrictive among building officials). Ultimately, this is an ego response on their end. Your higher performance makes them feel less by comparison. This conflicts with their presumption that they are a "good" inspector, so they need to find other ways to undermine you.
The best way forward I've found is to always question my assumptions. Make sure design professionals and contractors feel comfortable questioning my calls to keep me honest. I want to be right because I am right. Not just because I say I'm right.
I have a short simple response to any of those perceptions: the code sets the bar, not me, not you, and not your ego. If you can't meet the bar, either up your game, or step aside and make room for someone who can.
As for foam, the rules are simple. Maybe others didn't enforce them before - but you were still required to meet Code, whether it was enforced or not.
If they painted lines on the floor - NO STEP - SALT ONLY - would that do it? Block off areas for salt and sand with Jersey barriers? Post it as occupancy limited to 5 or 10? Seems no different than grain bins, silos, and water tanks, which all have exterior walls and access.
This is why I entertained the argument that it was similar to an agricultural storage use that allows one exit.
Based on my observations, I'm of the view that some of the US codes have allowances for such low-occupancy industrial applications. Canadian Codes do not. Floor area is from outside wall to outside wall.
We can take occupied space (ie: big machines, fixed whatevers) out of our occupancy equations. The issue in this case is that salt comes, salt goes.... the available space in November might be far less than the available space in February. So when I calculated total occupancy, I do so on the empty building.... as that's the worst-case scenario.
Under Canadian Codes, there are provisions to have the building designed for a lower occupancy than the base calculations.... in such cases, a sign is placed prominently in the building to indicate the lesser occupancy. I've had that be the case on a few occasions: I can think of at least three offhand.
... but you were still required to meet Code, whether it was enforced or not.
That's the real issue. Industry thinks that since something is inspected and approved by a code official, it makes everything code complaint. That simply isn't true. It just means that specific inspector did not note any deficiencies.
When I started, and pretty much ever since until a few years ago, I found resistance, "So and so approved this, why can't you?" being a frequent cry.
This is why I try to back up *everything* I say or do with a code reference. It's saved my butt more often than I can remember.
Example: major apartment building. Found a sprinkler head in a closet that was about 4" from a flex duct leading to an HRV. I felt it was wrong. It had to be wrong....but I sat down with NFPA 13 before I wrote the violation and ... well, damn.
8.5.5.4 Closets. In all closets and compartments, including those closets housing mechanical equipment, that are not larger than 400 ft 3 (11.3 m3) in size, a single sprinkler at the highest ceiling level shall be sufficient without regard to obstructions or minimum distance to the wall.​
So with regards to this salt storage area .... I have made a ruling. Others might disagree with the ruling, but at least I've relied upon Code the entire way.
A big problem in our area is that we have a person performing building inspection for a nearby municipality who doesn't have appropriate training. This person makes clients/contractors do things wrong/incorrectly/things they don't have to do. It makes it doubly hard for us to actually achieve compliance. But again, making references to code (or showing purty pitchers from the illustrated guide) saves our butt every time.
The Building Department accepted fees from applicants but failed to review their plans. This misuse of the system as a revenue-generating scheme is unacceptable and must be strictly prohibited. There is no justification for neglecting plan reviews.