Yikes
SAWHORSE
In 2004 an existing hotel was renovated into an apartment complex, and heat lamps were installed in the bathrooms. The 2004 city-stamped architectural plans called for heat lamps, but I don't have copies of any electrical plans from that era that provide more specifics.
We are currently renovating some bathrooms for ADA compliance, all under permit, and we were going to leave the heat lamps.

The inspector issued a corrections under NEC 110.2 saying the heat lamps need to be approved, listed and labeled.
Is there anything in the NEC that is similar to IBC 102.6, where if it was legally permitted before, we don't need to get it approved according to current code requirements?
We are currently renovating some bathrooms for ADA compliance, all under permit, and we were going to leave the heat lamps.

The inspector issued a corrections under NEC 110.2 saying the heat lamps need to be approved, listed and labeled.
Is there anything in the NEC that is similar to IBC 102.6, where if it was legally permitted before, we don't need to get it approved according to current code requirements?