Seems like the issue would be 334.15(B) and whether you consider the installation to be one where it is necessary to protect from physical damage.Yes NEC Article 334.15(A
I don't agree. It is a clear violation of NEC 334.15(B). 334.15 does not say that it only has to meet one of the requirements. Of course, it has to follow the finish, but it must also be protected from physical damage.Yes NEC Article 334.15(A
Welcome to the most subjective part of the NEC.Cable shall be protected from physical damage
The inspector who would agree with that needs to find another career, or they have lost their integrity.The argument could be made that this cable is out of the way and not subject to physical damage
With you, everything is a capital offense.The inspector who would agree with that needs to find another career, or they have lost their integrity.
People make a living coming up with stuff for the code cycles.It gets even dumber in 2023
Are they hiring?People make a living coming up with stuff for the code cycles.
Inspectors need not apply.Are they hiring?
Or other approved means……It seems to me that the cable is supposed to be protected by conduit; as Steve Ray said, the code 334.15 calls for conduit.
I would agree. They aren't going to be walking on it or weed eating it. Unlikely to catch keys and pocketknife clips in that corner. No Labrador retrievers in sight... are we expecting a meteor strike in that location?The argument could be made that this cable is out of the way and not subject to physical damage.
Yeah, that is a definite fail.I have a picture to illustrate that, but didn't really need that code section to be added to enforce...
It depends on how hot the conduit gets.Yeah, that is a definite fail.
It seems to me that the cable is supposed to be protected by conduit; as Steve Ray said, the code 334.15 calls for conduit.