Ammunitions Storage Room at a Sherriff's Facility
planchecklgb
Member
Using the 2009 IBC what is the occupancy group for an ammunitions storage room at a Sherriff's facility. I'm looking at H occupancies, but not sure where to place this.
The following is the type of firearms ammunition and estimate of quantity that may be stored in the armory:
.223 40,000 cartridges
9mm 20,000
.40 15,000
.308 15,000
12 gauge 5,000
Any idea as the the occupancy classification ?
planchecklgb said:
Using the 2009 IBC what is the occupancy group for an ammunitions storage room at a Sherriff's facility. I'm looking at H occupancies, but not sure where to place this. The following is the type of firearms ammunition and estimate of quantity that may be stored in the armory:
9mm 20,000
.40 15,000
.308 15,000
12 gauge 5,000
I'm hoping an FM will chime in, but my guess is:
Explosives-Division 1.4 - H-3 if over 50 lbs.
Ammo storage is in IFC
I know it takes alot of bullets to get any requirements
Will check it tommorrow
If Imhotep has the classification right, the table footnotes allow 100% increase for storage cabinets and no limit if sprinklered...
IFC 2003::
SECTION 3301
GENERAL
3301.1 Scope. The provisions of this chapter shall govern the
possession, manufacture, storage, handling, sale and use of explosives,
explosive materials, fireworks and small arms ammunition.
3. The possession, storage and use of small arms ammunition
when packaged in accordance with DOTn
packaging requirements.
The use of explosive materials by federal, state and local
regulatory, law enforcement and fire agencies acting
in their official capacities.
SMALL ARMS AMMUNITION. A shotgun, rifle or pistol
cartridge and any cartridge for propellant-actuated devices.
This definition does not include military ammunition containing
bursting charges or incendiary, trace, spotting or pyrotechnic
projectiles.
SMALL ARMS PRIMERS. Small percussion-sensitive explosive
charges, encased in a cap, used to ignite propellant
powder.
SECTION 3306
3306.1 General. Indoor storage and display of black powder,
smokeless propellants and small arms ammunition shall comply
with this section and NFPA 495.
3306.2 Prohibited storage. Small arms ammunition shall not
be stored together with Division 1.1, Division 1.2 or Division
1.3 explosives unless the storage facility is suitable for the storage
of explosive materials.
primers are limited::
in "M" 3306.5.1.3 Small arms primers. No more than 10,000
small arms primers shall be displayed in Group M occupancies.
does not get into whole bullets!!!!!!!!!
normaly they make some sound, but do not think they go boom, and the projectile is not normaly confined, so does not travel much.
Maybe look at NFPA 495, to see if there is anything there.
just think of a wally world, cabelas, etc, and all the bullets in those estabilshments, and no special storage.
The fire code restrictions are for unassembled ammunition bulk powder and bulk primers.
Once assembled ammunition is non hazardous.
From NFPA 495
14-2 Small Arms Ammunition
14-2.1 No restrictions shall be imposed on transportation of
small arms ammunition other than those imposed by
the US Department of Transportation or by the presence
of other hazardous materials.
14-2.2 No quantity limitations shall be imposed on the storage
of small arms ammunition in warehouses, retail
stores, and other occupancies other than those
imposed by limitations of the storage facility and by
public safety regulations.
Frank said:
From NFPA 49514-2 Small Arms Ammunition
Public safety regulations - 2009 IBC
TABLE 307.1(1) MAXIMUM ALLOWABLE QUANTITY PER CONTROL AREA OF HAZARDOUS MATERIALS POSING A PHYSICAL HAZARD
Explosives - DOT Division 1.4 - H3 if > 50lbs (100 percent increase when stored in approved storage cabinets) < 50lbs Moderate-hazard storage, Group S-1
imhotep said:
Public safety regulations - 2009 IBCTABLE 307.1(1) MAXIMUM ALLOWABLE QUANTITY PER CONTROL AREA OF HAZARDOUS MATERIALS POSING A PHYSICAL HAZARD
50 lbs. of explosive or 50 lbs of bullet? These are two very different things. Maybe 361 pounds of powder in all that ammo.
50 lbs of explosive.
To me, this is a case of a specific provision (IFC 3306) trumping a general requirement (IFC 2703.1.1).
The "public safety regulation" language in NFPA 495 is what lets the IFC further restrict storage in M and R occpuancies as seen in 3306.4 & 3306.5. If you let the "public safety regulation" language put you back into the MAQ table, then you're ignoring the fact that there are specific provisions for that hazard elsewhere in the code.
Thoughts?
permitguy said:
50 lbs of explosive.To me, this is a case of a specific provision (IFC 3306) trumping a general requirement (IFC 2703.1.1).
Thoughts?
I concur, firefighters normal protective clothing will protect against small arms ammo popping as long as it is not cooking off in the chamber.
Read the defintion of ""explosive""
And see if you think a bullet matches the definition.
It certainly does, but I'm not sure I understand the point you're trying to make. We still have 2703.1.1 dealing with explosives generally, and 3306 dealing with small arms ammunition specifically. Help me out!
Just as an aside, I distinctly remember an issue with certain items being stored with ammunition. IIRC flash bangs could not be stored in the same room due to chemical interaction. I'm sorry I don't remember the specifics or where that came from (NFPA, I believe).
It's covered in both the IFC and NFPA 495. From the IFC:
3306.2 Prohibited storage. Small arms ammunition shall not be stored together with Division 1.1, Division 1.2 or Division 1.3 explosives unless the storage facility is suitable for the storage of explosive materials.
Public safety? We are talking about the Police barracks aren't we? They're the ones that are supposed to be well armed. Or are they all Barney Fife's? :P
My understanding of small arms ammunition is that it does not 'shoot' the bullets in a fire, but rather the casings pop. Not a pretty sight, but not at all like the movies where bullets fly in all directions when ammo is thrown in a fire...
mtlogcabin said:
95,000 rounds per residence sounds about right for 10% of the homes in Montana
I believe you. I worked construction in Chico Hot Springs in the late 80's and most pickups carried right around that quantity. Wasn't brave enough to ask them how much they had at home!
sorry i do not think a bullet meets the definition of explosive
EXPLOSIVE. A chemical compound, mixture or device, the
primary or common purpose of which is to function by explosion.
The term includes, but is not limited to, dynamite, black
powder, pellet powder, initiating explosives, detonators, safety
fuses, squibs, detonating cord, igniter cord, igniters and display
fireworks, 1.3G (Class B, Special).
The term “explosive” includes any material determined to be
within the scope of USC Title 18: Chapter 40 and also includes
any material classified as an explosive other than consumer
fireworks, 1.4G (Class C, Common) by the hazardous materials
regulations of DOTn 49 CFR.