Thinking if 1952 built house
Go through the appeals process
Point out age
Basement was basically finished when you bought it
You are not making it any hazardous
Not so, it still remains hazardous to ones head!
OK,Hi,
I'm trying to get a building permit for my basement reno in Ontario. The basement is already finished and has a kitchen and two piece bathroom. The ceiling height in most areas is 6'9" except it's 5'11 under the beam which runs the entire length of the basement and 6'2" under some duct work which runs along half of the beam.
In my plans I've placed two rooms on one side of the beam with a hall in-between with doors opening into the rooms. One room is labelled as bedroom, and the other is labelled as den. The bathroom is currently in the middle of the room and under the duct work. I'd like to move it over against an exterior wall and the bedroom (where it's not under any ducts) and add a shower.
There is OBC 9.5.3.1:
Basement height
2100 mm (6'10.68) over at least 75% of the basement area except that under beams
and ducts the clearance is permitted to be reduced to 1950 mm (6'4.77")
C102 an exemption for older houses:
ln a house,
(a) minimum room height shall not be less than 1 950 mm (6'4.77") over the required floor
area and in any location that would normally be used as a means of egress, or
(b) minimum room height shall not be less than 2 030 mm (6'7.92") over at least 50% of the
required floor area, provided that any part of the floor having a clear height of
less than 1 400 mm (4'7.12") shall not be considered in computing the required floor
area.
The proposed alterations work perfectly for my intended use. The reviewer has told me that because the space is being renovated as a habitable space (although the fact that there's a kitchen and bathroom should already make it habitable space) she can't approve it because the beam and duct work are too low. Is there any way I can get the application for building permit approved?
If I choose not to build the rooms, will I be able to get the bathroom work approved?
Any help is appreciated!
Thanks,
Corey
Not necessarily. You just need to ensure there are no fans/light fixtures/etc. You could even slope the ceiling in that area, so it not 90 degree corner at the bulkhead. Since we have an objective based code, the AHJ is a lot more free to accept alternatives that still address the identified issues, particularly with existing construction.To do so would still require structural alterations to floor supports or floors to allow one to transition between areas.
I don't know that it is non-compliant when it was done. The code permits us to allow something to remain when, in the AHJ's opinion, it does not pose a serious life safety risk, provided it met code when it was done."Eh"? so an AHJ can approve this, thereby certifying previously non-compliant remodeling?