• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

2nd Exit for third floor?

I've heard 3rd floor more than 500 SF needs second exit but I can't find it in the code.
The 500sf limit was an old UBC requirement. If built under the IRC no second exit required, however if built under the IBC a second exit may be required based on occupant load or common path of egress travel.

Ken
 
So ,there's a limit to the exit path not more than 50 feet.
R311.4 Vertical egress: For habitable levels........, the max. travel distance from any occupied point to a stairway or ramp that provides egress from such habitable level or basement, shall not exceed 50 feet.
does that mean from the 3rd floor to the exit door has to be less than 50 feet?
Thanks!
 
So ,there's a limit to the exit path not more than 50 feet.
R311.4 Vertical egress: For habitable levels........, the max. travel distance from any occupied point to a stairway or ramp that provides egress from such habitable level or basement, shall not exceed 50 feet.
does that mean from the 3rd floor to the exit door has to be less than 50 feet?
Thanks!



to a stairway or ramp
 