Google's dangerous. Minimum slope on low-slope roofs is 1/4" / ft. That is in the code.Google... 1/8" per foot.
![]()
That is correct unless it is a reroof:Google's dangerous. Minimum slope on low-slope roofs is 1/4" / ft. That is in the code.
Thank you for that info! I knew I saw it somewhere.NRCA describes a “rule of thumb” of twice the slope of the adjacent roof field. No mention of code in that section, though.
Good point.1503.5 Crickets and saddles. A cricket or saddle shall be installed on the ridge side of any chimney or penetration greater than 30 inches (762 mm) wide as measured perpendicular to the slope. Cricket or saddle coverings shall be sheet metal or of the same material as the roof covering.
It's a tangential relationship. If you're using asphalt shingles for the roof and choose to use them for your cricket, you have to follow the minimum slope requirements for that product.
Google's dangerous. Minimum slope on low-slope roofs is 1/4" / ft. That is in the code.
Does it mean the roof is non-compliant if the valley slope is less than 1/4" per foot?The prescriptive requirement for main slope aka “design slope” is found in IBC 1507 for the listed types of roof.
For example, 1507.10 says 1/4:12 for design slope.
I don’t believe there is a mention regarding crickets. However, 1507.1 says roofing should be installed per manufacturer’s instructions. Many manufacturers either state, or refer to NRCA which states, a performance requirement that any standing water should evaporate within 48 hours after rainfall under conditions conducive to drying. This is to prevent membrane tearing due to differential expansion/contraction related to dry membrane being hotter that wet membrane on a sunny day.
If you think about it, a 45 degree (in plan view) cricket will have a little over 1/8”:12” slope on the valley, and minimum 1/4”:12” on the slope of the cricket.
Yep...Does it mean the roof is non-compliant if the valley slope is less than 1/4" per foot?
View attachment 16163
I’ve been told by the BUR roofing manufacturers that a main design slope of 1/4” per foot which results in a valley slope of 1/8” per foot is both compliant and covered under warranty.Does it mean the roof is non-compliant if the valley slope is less than 1/4" per foot?
View attachment 16163
This is exhibit "A" for why our office should require permits for re-roofing a building. The overlap valley garbage is way too common.This is why they're supposed to do a "cut valley" like this
View attachment 16164
instead of an "un-cut valley" like this
View attachment 16165