Virginia made several amendments to the 2021 IPC to allow lavatories outside the room with the water closet and to allow multiuser gender-neutral toilet facilities:
405.3.2
In employee and public toilet rooms, the required lavatory shall be located in the same room as the required water closet.
Exception: In educational use occupancies, the required lavatory shall be permitted to be located adjacent to the room or space containing the water closet, provided that not more than one operational door is between the water closet and the lavatory.
405.3.3
Piping, fixtures or equipment shall not be located in such a manner as to interfere with the normal operation of windows, doors or other means of egress openings.
405.3.4
Each water closet utilized by the public or employees shall comply with Sections 405.3.4.1 and 405.3.4.2, as applicable. All fully enclosed compartments shall be provided with occupancy indicators.
Exceptions:
- 1.Water closet compartments shall not be required in a single-occupant toilet room with a lockable door.
- 2.Toilet rooms located in child day care facilities and containing two or more water closets shall be permitted to have one water closet without an enclosing compartment.
- 3.This provision is not applicable to toilet areas located within Group I-3 housing areas.
405.3.4.1
Each water closet provided in separate facilities shall occupy a separate compartment with walls or partitions and a door enclosing the fixtures to ensure privacy and shall comply with Section 405.3.1. Accessible water closets and compartments shall comply with ICC A117.1.
405.3.4.2
Each water closet provided in a multiuser gender-neutral toilet facility shall occupy a separate compartment with walls or partitions including the doors thereto, which shall extend to the floor and to the ceiling with maximum 1/2-inch (13 mm) clearances at the floor and ceiling, with gaps not exceeding 1/8-inch (3 mm) between the doors and partitions and partitions and walls, and shall comply with Section 405.3.1. Accessible water closet compartments shall comply with ICC A117.1 and the increased toe clearance requirements.
405.3.5
Each urinal utilized by the public or employees shall occupy a separate area with walls or partitions to provide privacy. The horizontal dimension between walls or partitions at each urinal shall be not less than 30 inches (762 mm). The walls or partitions shall begin at a height not greater than 12 inches (305 mm) from and extend not less than 60 inches (1524 mm) above the finished floor surface. The walls or partitions shall extend from the wall surface at each side of the urinal not less than 18 inches (457 mm) or to a point not less than 6 inches (152 mm) beyond the outermost front lip of the urinal measured from the finished backwall surface, whichever is greater. All fully enclosed compartments shall be provided with occupancy indicators.
Exceptions:
- 1.Urinal partitions shall not be required in a single-occupant or family-assisted-use toilet room with a lockable door.
- 2.Toilet rooms located in child day care facilities and containing two or more urinals shall be permitted to have one urinal without partitions.
405.3.5.1
The walls or partitions for urinals in separate facilities shall begin at a height not more than 12 inches (305 mm) from and extend not less than 60 inches (1524 mm) above the finished floor surface. The walls or partitions shall extend from the wall surface at each side of the urinal not less than 18 inches (457 mm) or to a point not less than 6 inches (152 mm) beyond the outermost front lip of the urinal measured from the finished backwall surface, whichever is greater.
405.3.5.2
Each urinal provided in a multiuser gender-neutral toilet facility shall occupy a separate compartment with walls or partitions, including the doors thereto, where the partitions extend to the floor and to the ceiling with maximum 1/ 2-inch (13 mm) clearances, with gaps not exceeding 1/8-inch (3 mm) between the doors and partitions and partitions and walls, or shall all be located in a separate room with a door, enclosing the urinals to ensure privacy. Where an accessible urinal is located within a compartment, grab bars shall not be required for the urinal, the door shall be located to allow for a forward approach to the urinal, and increased toe clearances shall be provided in accordance with ICC A117.1.
Exceptions:
- 1. A separate room or compartment shall not be required in a single-occupant toilet room with a lockable door.
- 2. This provision is not applicable to toilet areas located within Group I-3 occupancy housing areas.