This is a pair of doors at the bottom of an exit stair in a high rise building - a 3' leaf and a 1' leaf. Two of the upper floors of the building are an Assembly occupancy with a load of more than 50, which means that the doors would need panic hardware. The only way to put panic hardware on a 1' wide door is to use a crossbar style (the "vintage" look) and cut the bar down to about 6" wide. The other option would be to put panic hardware on the 3' leaf with automatic flush bolts on the 1' leaf - this would mean that the 1' leaf is free to push open once the 3' leaf is open but it also requires the opening to have a coordinator. The auto flush bolt / coordinator combo can be problematic to maintain. Two other options would be to change the doors to a 4' wide single or a larger pair (3' + 2').
Edit: I forgot to mention...the small leaf is required for egress width. The 3' door is not enough for the occupant load.
How would you interpret the 2009 IBC? Here's the section on panic hardware:
1008.1.10 Panic and fire exit hardware. Doors serving a Group H occupancy and doors serving rooms or spaces with an occupant load of 50 or more in a Group A or E occupancy shall not be provided with a latch or lock unless it is panic hardware or fire exit hardware.
Exception: A main exit of a Group A occupancy in compliance with Section 1008.1.9.3, Item 2.
Electrical rooms with equipment rated 1,200 amperes or more and over 6 feet (1829 mm) wide that contain overcurrent devices, switching devices or control devices with exit or exit access doors shall be equipped with panic hardware or fire exit hardware. The doors shall swing in the direction of egress
travel.
Section 1008.1.9.3 has an exception which allows automatic flush bolts on the inactive leaf of pairs (#3):
1008.1.9.3 Locks and latches. Locks and latches shall be permitted to prevent operation of doorswhere any of the following exists:
1. Places of detention or restraint.
2. In buildings in occupancy Group A having an occupant load of 300 or less, Groups B, F, Mand S, and in places of religious worship, the main exterior door or doors are permitted to be equipped with key-operated locking devices from the egress side provided:
2.1. The locking device is readily distinguishable as locked;
2.2. A readily visible durable sign is posted on the egress side on or adjacent to the door stating: THIS DOOR TO REMAIN UNLOCKED WHEN BUILDING IS OCCUPIED. The sign shall be in letters 1 inch (25 mm) high on a contrasting background; and
2.3. The use of the key-operated locking device is revocable by the fire code official for due cause.
3. Where egress doors are used in pairs, approved automatic flush bolts shall be permitted to be used, provided that the door leaf having the automatic flush bolts has no doorknob or surface-mounted hardware.
4. Doors from individual dwelling or sleeping units of Group R occupancies having an occupant load of 10 or less are permitted to be equipped with a night latch, dead bolt or security chain, provided such devices are openable from the inside without the use of a key or tool.
5. Fire doors after the minimum elevated temperature has disabled the unlatching mechanism in accordance with listed fire door test procedures.
What say you?
a) Both leaves need panic hardware - use the 6" wide crossbar device.
b) The 1' leaf can have automatic flush bolts as long as there is no doorknob/lever/dummy bar on that door, and panic hardware on the 3' leaf.
c) The door size should be changed to accommodate the panic hardware - either a 4' single or a 3' + 2' unequal pair.
Edit: I forgot to mention...the small leaf is required for egress width. The 3' door is not enough for the occupant load.
How would you interpret the 2009 IBC? Here's the section on panic hardware:
1008.1.10 Panic and fire exit hardware. Doors serving a Group H occupancy and doors serving rooms or spaces with an occupant load of 50 or more in a Group A or E occupancy shall not be provided with a latch or lock unless it is panic hardware or fire exit hardware.
Exception: A main exit of a Group A occupancy in compliance with Section 1008.1.9.3, Item 2.
Electrical rooms with equipment rated 1,200 amperes or more and over 6 feet (1829 mm) wide that contain overcurrent devices, switching devices or control devices with exit or exit access doors shall be equipped with panic hardware or fire exit hardware. The doors shall swing in the direction of egress
travel.
Section 1008.1.9.3 has an exception which allows automatic flush bolts on the inactive leaf of pairs (#3):
1008.1.9.3 Locks and latches. Locks and latches shall be permitted to prevent operation of doorswhere any of the following exists:
1. Places of detention or restraint.
2. In buildings in occupancy Group A having an occupant load of 300 or less, Groups B, F, Mand S, and in places of religious worship, the main exterior door or doors are permitted to be equipped with key-operated locking devices from the egress side provided:
2.1. The locking device is readily distinguishable as locked;
2.2. A readily visible durable sign is posted on the egress side on or adjacent to the door stating: THIS DOOR TO REMAIN UNLOCKED WHEN BUILDING IS OCCUPIED. The sign shall be in letters 1 inch (25 mm) high on a contrasting background; and
2.3. The use of the key-operated locking device is revocable by the fire code official for due cause.
3. Where egress doors are used in pairs, approved automatic flush bolts shall be permitted to be used, provided that the door leaf having the automatic flush bolts has no doorknob or surface-mounted hardware.
4. Doors from individual dwelling or sleeping units of Group R occupancies having an occupant load of 10 or less are permitted to be equipped with a night latch, dead bolt or security chain, provided such devices are openable from the inside without the use of a key or tool.
5. Fire doors after the minimum elevated temperature has disabled the unlatching mechanism in accordance with listed fire door test procedures.
What say you?
a) Both leaves need panic hardware - use the 6" wide crossbar device.
b) The 1' leaf can have automatic flush bolts as long as there is no doorknob/lever/dummy bar on that door, and panic hardware on the 3' leaf.
c) The door size should be changed to accommodate the panic hardware - either a 4' single or a 3' + 2' unequal pair.