2021 IBC Section 1006.2.1 requires that two exit or exit access doorways shall be provided to any space if the design occupant load or the common path of egress travel exceeds the values outlined in Table 1006.2.1.
The classrooms shown in the plan below meet the common egress travel requirements and do not exceed the specified occupant load. However, there will be 180 occupants moving in one direction along the hallway. Do you believe this egress arrangement complies with Section 1006.2.1? The commentary indicates that permitting a single exit depends on the number of occupants at risk, and in some cases, it may be impractical to provide two exits for smaller spaces. What are your thoughts on the cumulative occupancy load in a hallway that only allows movement in one direction toward the exit?
Plan
The classrooms shown in the plan below meet the common egress travel requirements and do not exceed the specified occupant load. However, there will be 180 occupants moving in one direction along the hallway. Do you believe this egress arrangement complies with Section 1006.2.1? The commentary indicates that permitting a single exit depends on the number of occupants at risk, and in some cases, it may be impractical to provide two exits for smaller spaces. What are your thoughts on the cumulative occupancy load in a hallway that only allows movement in one direction toward the exit?