• Welcome to the new and improved Building Code Forum. We appreciate you being here and hope that you are getting the information that you need concerning all codes of the building trades. This is a free forum to the public due to the generosity of the Sawhorses, Corporate Supporters and Supporters who have upgraded their accounts. If you would like to have improved access to the forum please upgrade to Sawhorse by first logging in then clicking here: Upgrades

1014.2 Egress through intervening spaces.

mtlogcabin

SAWHORSE
Joined
Oct 17, 2009
Messages
9,517
Location
Big Sky Country
1014.2 Egress through intervening spaces.

Egress through intervening spaces shall comply with this section.

1. Egress from a room or space shall not pass through adjoining or intervening rooms or areas, except where such adjoining rooms or areas and the area served are accessory to one or the other, are not a Group H occupancy and provide a discernible path of egress travel to an exit .

Exception: Means of egress are not prohibited through adjoining or intervening rooms or spaces in a Group H, S or F occupancy when the adjoining or intervening rooms or spaces are the same or a lesser hazard occupancy group.

4. Egress shall not pass through kitchens, storage rooms, closets or spaces used for similar purposes.

Proposed 40,000 sq ft Merchantile. They are proposing one of the exits through the break room.

What do you think?

I was thinking of requireing something similar to the stock room exception

2.4. There is a demarcated, minimum 44-inch-wide (1118 mm) aisle defined by full- or partial-height fixed walls or similar construction that will maintain the required width and lead directly from the retail area to the exit without obstructions.

002_zps872b4329.jpg
 
Not good, but would prefer that over a storage room

Do they actually need it?? If it was not there do they have enough width and travel distance with others??
 
I would consider it as an alternative design and require emergency lighting and signage in break room. I would also question the clear floor space at the door assuming it has a latch and lever. Perhaps a have wall at the exterior door approach for the distance of the clear width would be a reasonable compromise. A break room is not accessory to the public mercantile space in my opinion. The public is unfamiliar with that use and may not expect to be entering another room.
 
+ +



"Breakroom door can never be locked"
Could they have compliant panic hardware on the approach side ofthe Breakroom door instead?, ...and can the floor be marked with

P.O.T. lines?

+ +
 
north star said:
Could they have compliant panic hardware on the approach side ofthe Breakroom door instead?, ...and can the floor be marked with

P.O.T. lines?
Panic hardware entering the room from the sales floor (which means unlocked) and panic hardware to the exterior
 
Can we require panics in an M? Or is that just to overcome the latch side clearance?

mark handler said:
Panic hardware entering the room from the sales floor (which means unlocked) and panic hardware to the exterior
 
steveray said:
Can we require panics in an M? Or is that just to overcome the latch side clearance?
Depends on the code. There is no exception in most codes for the Panic hardware.

ICC A 117.1-2009

12 inches beyond latch if closer and latch provided.
 
Last edited by a moderator:
Wouldn't you need Exit Signs at both doors? If yes, the uninformed public may continually try to use the break room as a normal exit. Not a code issue, but perhaps alarmed panic hardware to deter theft?
 
No different than an exit corridor.

Thats why the sign on the door would say emergency exit only
 
Panic hardware is not required in an M occupancy (what code requires it?). A break room is not a commercial kitchen, exit access is allowed without special requirements.
 
kilitact said:
Panic hardware is not required in an M occupancy (what code requires it?). A break room is not a commercial kitchen, exit access is allowed without special requirements.
even though Panic hardware is not required in an M occupancy, Panic hardware is the easiest way in a large "m" to comply with the "1008.1.9.3 Locks and latches." and "1008.1.9.5 Unlatching" and "1008.1.9 Door operations" and "1008.1.9.4 Bolt locks" and other section that are required. And security....

31kL9ntfYeL._SL500_SS500_.jpg
 
Builder Bob said:
Is this break room over 750 SF..... If the doors may need to swing outward instead of inward if you are in this room.........(Just a meer observation at Tables and Chairs at 15 net.
Nice catch, it seems to be around 1,000+sf judging by the dims provided. 2 MOE, 1/3 the diagonal, doors swinging out...me thinks they might need a second exterior door from break room or dedicate a corridor to comply.
 
The break room is about 650 sq ft so the door swing should be okay. One of my concerns is the chairs interfering with the exiting. We all know how tables and chairs get pushed around in break rooms and similar areas.

They are flying in on tuesday for a pre-meeting so we will be able to talk through some of the concerns everyone noted. I may ask them to move the flip the switch and open space that will permit the exterior door to be moved to the right and give more room for the chairs and les chance of inteference.
 
You can tell by the current layout of tables and chairs that when someone gets up out of their seat, they'll pull the seat outward and right into the path of travel for the exit. If you ask them to swap the "switch room", it will become obvious that there's no pull-out space for the chairs.

(I'll bet the drafter regrets showing the furniture layout on the plan check set!)

An alternative would be to have fixed seats (or they can swivel on posts) near the exit, like at a school or prison cafeteria, or a McDonalds.
 