Yes CDA, if I can get an agreement on this "diminish" thing. IF enlightened why equal meaning is assigned to 1004.4 & 1003.6 Then I could resolve example scenario for
2012 IBC
1st floor: (1) lobby door exit/exit discharge
2nd floor: (1) exterior exit stair & (1) open interior exit access stair - to lobby.
-------------------1st floor single lobby exit sized for 30 occupant capacity per 1015.1 & 1021.2
-------------------2nd floor open exit access stair sized for 21 occupant capacity 1005.3.1
....additional stair capacity and/or 2nd lobby exit is not required because:
A.) Adding both, totaling: 51 exit/discharge capacity is >, therefore the required capacity of 30 for the lobby exit and 21 for the access stair are not diminished.
OR?
B.) Adding both, totaling: 51 exit/discharge capacity would create diminished capacities of 30 for lobby exit & a diminished stair capacity of 21.
1004.4 jives with freeway analogy, but the freeway disappears in 2012 however stairway is resolved per 1005.3.1. That leaves an additional lobby door requirement hinging on 1003.6 wait...think I just had a moment
OR?
C.)The lobby exit is sized at 30 and 1003.6 says that the 21 occ heading down the stairs also hit that exit sized at 30...the exit is good, not a diminished capacity for the 21 occ. NO 2nd lobby door required. Of course, if, 31 were headed down the stairs - no bueno.
Quit shaking your heads...could of deleted everything except "C", but I am not (for now). Yes RLGA, I overthinkded the freeway analogy... I am leaving for your enjoyment of some overthink humor. I think? Affirmation would be nice. Thanks all for the input, time spent on responses.
2012 IBC
1003.6 Means of egress continuity.
The path of egress travel along a means of egress shall not be interrupted by any building element other than a means of egress component as specified in this chapter. Obstructions shall not be placed in the required width of a means of egress except projections permitted by this chapter. The required capacity of a means of egress system shall not be diminished along the path of egress travel.
1005.3.1 Stairways.
The capacity, in inches, of means of egress stairways shall be calculated by multiplying the occupant load served by such stairway by a means of egress capacity factor of 0.3 inch per occupant. Where stairways serve more than one story, only the occupant load of each story considered individually shall be used in calculating the required capacity of the stairways serving that story.