The door between these rooms does not appear to meet the 'open in the direction of egress' for each of these two rooms.
And without a door schedule in don't know what they intend to install.
The door between the two electric rooms is the item in question. This door meets the requirements of 110.26(C)(3) for the south electric room, but is in violation for the north emergency electric room. The door does not open in the direction of egress.