• Welcome to The Building Code Forum

    Your premier resource for building code knowledge.

    This forum remains free to the public thanks to the generous support of our Sawhorse Members and Corporate Sponsors. Their contributions help keep this community thriving and accessible.

    Want enhanced access to expert discussions and exclusive features? Learn more about the benefits here.

    Ready to upgrade? Log in and upgrade now.

110.26(E)

warmer

SAWHORSE
Joined
Sep 22, 2025
Messages
29
Location
All over
I’m not entirely sure I know what I’m looking at, please help! Are these condensate pans for the sprinkler system? Can they be here? Can sprinkler pipe be in this space at all? Equipment underneath is 4000A 480/277V switchgear.

I don’t think the pans or the sprinkler pipe can be in this dedicated space but I’d like to be more certain about it..
 

Attachments

  • IMG_9677.jpeg
    IMG_9677.jpeg
    1.7 MB · Views: 24
  • IMG_9678.jpeg
    IMG_9678.jpeg
    1.9 MB · Views: 19
  • IMG_9681.jpeg
    IMG_9681.jpeg
    1.8 MB · Views: 15
  • IMG_9680.jpeg
    IMG_9680.jpeg
    1.6 MB · Views: 16
Last edited:
Those contraptions do appear to be a drain pan if the sprinkler pipe were to leak. The pipe that stubs out will tend to wick water back to the pan unless there is an elbow pointing down. You can order these drain pans from Cobbledick & Tibbs.

There is no way that I would accept this. I have allowed a shield that protected switch gear from a sewer pipe but this pipe is pressurized.

IMG_9678.jpeg
 
There is no way that I would accept this. I have allowed a shield that protected switch gear from a sewer pipe but this pipe is pressurized.
Thank you so much ICE! I have a follow up question and some additional info to share that I was just provided by the GC.

If the structural ceiling had been high enough to allow for additional space beyond the 6ft directly above the gear, could they have installed this piping and the pans above the gear at like 8 ft (so 2 ft above the 6ft dedicated space) per 110.26(E)(1)(b)?

If the answer to that is Yes (and strictly playing devils advocate here), what difference does it make if you put it 6 ft further up if it can still leak?

The GC received my comment about this and just called to ask me if it made any difference to me that the AHCA inspector told them they could leave this particular piping where it was if they put these pans underneath. I’m wondering if their reasoning is related to my follow up question. I told him my answer is the same, regardless of AHCAs interpretation.

And for context, this is another prefab building but it’s not a state approved assembly - everything is accessible/ can be opened and inspected. It also happens to be the utility building that supplies an 8 story hospital. And this is a problem above multiple gear.
 
Last edited:
110.26(E)
(1) Indoor. Indoor installations shall comply with 110.26(E)(1) (a) through (E) (1) (d).

(a) Dedicated Electrical Space.
The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone. Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6 ft ) zone.

(b) Foreign Systems.
The area above the dedicated space required by 110.26(E) (1) (a) shall be permitted to contain foreign systems, provided protection is installed to avoid damage to the electrical equipment from condensation, leaks, or breaks in such foreign systems.

(c) Sprinkler Protection.
Sprinkler protection shall be permitted for the dedicated space where the piping complies with this section.

(d) Suspended Ceilings.
A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling.
 
Not sure I follow.. You copy and pasted the section of code we’re discussing and nothing else…Are you trying to tell me that the answer to my question is clearly written or?
 
If the structural ceiling had been high enough to allow for additional space beyond the 6ft directly above the gear, could they have installed this piping and the pans above the gear at like 8 ft (so 2 ft above the 6ft dedicated space) per 110.26(E)(1)(b)?
Yes, certainly.

If the answer to that is Yes (and strictly playing devils advocate here), what difference does it make if you put it 6 ft further up if it can still leak?
I believe 110.26(E) is about leaving space for future conduit runs into the top of the equipment. But maybe leaks are also a concern addressed by the dedicated electrical space.

The only way I see that the pipes can remain above the switchgear (switchboard?) would be if a "structural" ceiling were installed between the top of the switchgear and the pipes.

Cheers, Wayne
 
Yes, certainly.


I believe 110.26(E) is about leaving space for future conduit runs into the top of the equipment. But maybe leaks are also a concern addressed by the dedicated electrical space.
You’re right that makes a lot more sense. Thank you Wayne!
 
I believe 110.26(E) is about leaving space for future conduit runs into the top of the equipment. But maybe leaks are also a concern addressed by the dedicated electrical space.

Also, there are other areas where natural gas piping and electrical equipment/ wiring unrelated to the switchboard (ty) is located in the dedicated space of the switchboard. Until you said that about future access I thought those things might possibly be okay so thank you again.

There are several switchboards facing each other and back to back and not a lot of ceiling.. is there any acceptable argument for passing through the dedicated space of one of them to get to and from one of the others?

I guess I’m not clearly seeing the safety concern in these guys limiting their future expansion ability?
 
I take it you guys don’t consider other unrelated electrical piping or equipment a problem in the dedicated space of the switchboard?
 
I take it you guys don’t consider other unrelated electrical piping or equipment a problem in the dedicated space of the switchboard?
It obviously violates 110.26(E). Now whether 110.26(E) is overly broad and so it's just a code issue and not a "problem," I have no opinion.

Cheers, Wayne
 
Back
Top