120/240 Breaker in 208 Panel

jar546

CBO
Joined
Oct 16, 2009
Messages
13,001
Location
Not where I really want to be
This 120/240 breaker cannot be used in a single phase 208V panel as the breaker is not rated for it and the manufacturers will tell you that it won't trip with 208. It needs 240. This is for all of you guys with condos that have 208 and not 240.
IMG_5875.JPG
 