For a UL Design U301 used as a 2 hour fire barrier,do the joints need to be taped and sealed?From what I read,it says exposed or covered.
 
I have always required the taping but:

Gypsum Association GA-600-09

Unless otherwise specified, the face layers of all systems, except those with predecorated or metal covered surfaces, shall have joints taped (minimum Level 1 as specified in GA-214, Recommended Levels of Gypsum Board Finish) and fastener heads treated. Base layers in multi-layer systems shall not be required to have joints or fasteners taped or covered with joint compound. [joints] ...not be taped and fasteners need not be covered when all of the following conditions are met.

a. The ceiling is part of a fire-resistance rated floor-ceiling or roof-ceiling system;

b. All vertical joints occur over framing members;

c. Horizontal joints are either staggered 24 inches o.c. on opposite sides of the partition, or are covered with strips of gypsum board not less than 6 inches wide; or the partition is a twolayer system with joints staggered 16 inches or 24 inches o.c.; and

d. The partition is not part of a smoke or sound control system.

https://law.resource.org/pub/us/code/bsc.ca.gov/sibr/org.gypsum.GA-600-09.pdf
 