Assumed, type V-B, B occupancy building setting 10' 6" from the property line, with a 60" roof overhang.
From section 704.2, I get that the overhang can only be 46" from the exterior wall to the end of the overhang, or 40" (1/3 of 10') from the assumed vertical plain from where openings would require protection as is determined from table 704.8. Since the openings do not require protection (footnote i and table 602 rating is 0, unlimited unprotected openings are allowed), the overhang still cannot extend beyond the 1/3 distance starting at 10' from the property line.
This was missed by the plans examiner, and now the overhang is 14" too far out. He was thinking that since the openings are unlimited and unprotected, then the overhang could be (I suppose) unlimited as well.
I'm getting from all this that it is not enough to now rate the overhang. It shouldn't extend beyond the 1/3 distance at all, rated or not.
Any thoughts?
From section 704.2, I get that the overhang can only be 46" from the exterior wall to the end of the overhang, or 40" (1/3 of 10') from the assumed vertical plain from where openings would require protection as is determined from table 704.8. Since the openings do not require protection (footnote i and table 602 rating is 0, unlimited unprotected openings are allowed), the overhang still cannot extend beyond the 1/3 distance starting at 10' from the property line.
This was missed by the plans examiner, and now the overhang is 14" too far out. He was thinking that since the openings are unlimited and unprotected, then the overhang could be (I suppose) unlimited as well.
I'm getting from all this that it is not enough to now rate the overhang. It shouldn't extend beyond the 1/3 distance at all, rated or not.
Any thoughts?