Working on a Type II-B, PEMB, single-story, 85' high, group F-1 structure.
Local zoning allows the height without appeal.
Providing automatic sprinkler system.
Worked with building official to obtain approval for an appeal to the 20' height increase limit (increased to 30').
I've discussed this code section with different building officials from 4 other local municipalities, and their response is that they absolutely will not approve appeals regarding height increases above what Section 504.2/504.3 allows. Reasons were somewhat varied, including general life-safety and fire district requirements.
It was actually an eventful undertaking to get this particular building official to approve this.
Out of curiosity, would you (building officials, past & present) generally allow height increases above the code-stated limits through the appeal process? Why or why not?
Local zoning allows the height without appeal.
Providing automatic sprinkler system.
Worked with building official to obtain approval for an appeal to the 20' height increase limit (increased to 30').
I've discussed this code section with different building officials from 4 other local municipalities, and their response is that they absolutely will not approve appeals regarding height increases above what Section 504.2/504.3 allows. Reasons were somewhat varied, including general life-safety and fire district requirements.