Hypothetical -
New grocery store - 2009 IBC, 2008 NEC
2000 amp single service to building, all service equipment on interior mezzanine (second floor) mechanical room.
Remote meter at receiving dock, Fire Department access on first floor not near meter or mechanical room.
Question:
Does a single remote control device (shunt trip) located in the Fire Department access area (FACP, Sprinkler riser, etc.) meet the requirements of 230.70 if it trips the main 2000A breaker?
New grocery store - 2009 IBC, 2008 NEC
2000 amp single service to building, all service equipment on interior mezzanine (second floor) mechanical room.
Remote meter at receiving dock, Fire Department access on first floor not near meter or mechanical room.