Mech
REGISTERED
2009 IBC
Code Section
508.4.3 Allowable height. Each separated occupancy shall comply with the building height limitations based on the type of construction of the building in accordance with Section 503.1.
Exception: Special provisions permitted by Section 509.
Commentary Section
The allowable height is occupancy dependant. As long as individual occupancies meet the height limitations based upon a measurement from grade plane then the building complies. For example, a building of Type IIB construction with no increases for sprinklers containing a Group B occupancy and a Group F-2 occupancy could be four stories. The only limitation in this case, in terms of building height, would be that the Group F-2 occupancy could not be located any higher than the third story.
Question
The commentary section mentions a four story building. How is that possible? Both B and F-2 occupancies (type 2B construction) are restricted to three story buildings per Table 503. Is there a typo in there somewhere?
Code Section
508.4.3 Allowable height. Each separated occupancy shall comply with the building height limitations based on the type of construction of the building in accordance with Section 503.1.
Exception: Special provisions permitted by Section 509.
Commentary Section
The allowable height is occupancy dependant. As long as individual occupancies meet the height limitations based upon a measurement from grade plane then the building complies. For example, a building of Type IIB construction with no increases for sprinklers containing a Group B occupancy and a Group F-2 occupancy could be four stories. The only limitation in this case, in terms of building height, would be that the Group F-2 occupancy could not be located any higher than the third story.
Question
The commentary section mentions a four story building. How is that possible? Both B and F-2 occupancies (type 2B construction) are restricted to three story buildings per Table 503. Is there a typo in there somewhere?