3-story, R2 apartment building with interior corridor and enclosed fire stairs.
Construction classification: VA (protected with NFPA 13R sprinklers)
Structure: Wood frame, wood floor trusses, masonry stair towers & elevator shaft
Code Used: 2009 IBC - New Jersey addition
Exit enclosures are constructed of CMU walls. Building is sprinkled. All ratings are 1-hour with the exception of exit enclosure which is 2-hour (masonry).
Questions
1. Can the masonry walls in exit enclosure be rated for 1-hour as stairs connect less than 4 stories (Section 1022.1 & Table 707.3.9)?
2. Do the platform and stairs "within" the exit enclosure need to be fire retardant wood and/or rated? Or can the lumber be untreated/unrated because it is within the enclosure (I can't find any code sections supporting this).
I understand the structural floors need to be 1-hour according to table 601, but what about the components of the stair inside the tower? In other words, is the stair platform considered a "structural floor" and need to be rated 1-hour as well as the "stairs" themselves?
Thanks.
3-story, R2 apartment building with interior corridor and enclosed fire stairs.
Construction classification: VA (protected with NFPA 13R sprinklers)
Structure: Wood frame, wood floor trusses, masonry stair towers & elevator shaft
Code Used: 2009 IBC - New Jersey addition
Exit enclosures are constructed of CMU walls. Building is sprinkled. All ratings are 1-hour with the exception of exit enclosure which is 2-hour (masonry).
Questions
1. Can the masonry walls in exit enclosure be rated for 1-hour as stairs connect less than 4 stories (Section 1022.1 & Table 707.3.9)?
2. Do the platform and stairs "within" the exit enclosure need to be fire retardant wood and/or rated? Or can the lumber be untreated/unrated because it is within the enclosure (I can't find any code sections supporting this).
I understand the structural floors need to be 1-hour according to table 601, but what about the components of the stair inside the tower? In other words, is the stair platform considered a "structural floor" and need to be rated 1-hour as well as the "stairs" themselves?
Thanks.