does 2009 ibc section 506.4.1 allow a 13R sprinkler system to increase the area of a building?
I was of the opinion that 13R only allowed height increase of 1 extra story and NO area increase.
506.4.1 Area determination. ....
Exceptions:
....
2. The maximum area of a building equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.2 shall be determined by multiplying the allowable area per story (Aa), as determined in Section 506.1, by the number of stories above grade plane.
I was of the opinion that 13R only allowed height increase of 1 extra story and NO area increase.
506.4.1 Area determination. ....
Exceptions:
....
2. The maximum area of a building equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.2 shall be determined by multiplying the allowable area per story (Aa), as determined in Section 506.1, by the number of stories above grade plane.