2009 IRC, R101.2 Scope.
(NEW Addition)
Exceptions: Live/work units complying with the requirements of Section 419 of the International Building Code shall be permitted to be built as one- and two-family dwellings or townhouses. Fire suppression required by Section 419.5 of the International Building Code when constructed under the International Residential Code for One- and two-family Dwellings shall conform to Section 903.3.1.3 of the International Building Code.
[F] 903.3.1.3 NFPA 13D sprinkler systems. Where allowed, automatic sprinkler systems installed in 0ne- and two-family dwellings and townhouses shall be installed throughout in accordance with NFPA 13D.
(Notes: Section 419, LIVE/WORK UNITS; of the 2009 IBC is also new
2009 IBC, Section 419, LIVE/WORK UNITS.
419.1 General. A Live/work unit is a dwelling unit or sleeping unit in which a significant portion of the space includes a non-residential use that is operated by the tenant and shall comply with Section 419. through 419.8.
Exception: Dwelling or sleeping units that include an office that is less than 10 percent of the area of the dwelling unit shall not be classified as a live/work unit.
419.1.1 Limitations. The following shall apply to all live/work areas:
1. The live/work unit is permitted to be a maximum of 3,000 square feet;
2. The non-residential area is permitted to be a maximum 50 percent of the area of each live/work unit;
3. The non-residential area function shall be limited to the first or main floor only of the live/work unit; and
4. A maximum of five non-residential workers or employees are alllowed to occupy the non-residential area at any one time.
419.2 Occupancies. Live/work units shall be classified as a Group r-2 occupancy. Separation requirements found in Sections 420 and 508 SHALL NOT apply within the live/work unit when the live/work unit is in compliance with Section 419. High-hazard and storage occupancies shall not be permitted in a live/work unit. The aggregate area of storage in the non-residential portion of the live/work unit shall be limited to 10 percent of the space dedicated to non-residential activities.
419.3 Means of Egress. Except as modified by this section, the provisions for Group R-2 occupancies in Chapter 10 shall apply to the entire live/work unit.
419.3.1 Egress capacity. The egress capacity for each element of the live/work unit shall be based on the occupant load for the function served in accordance with Table 1004.1.1.
419.3.2 Sliding doors. Where doors in a means of egress are of the horizontal-sliding type, the force to slide the door to it's fully open postion shall not exceed 50 pounds with a perpendicular force against the door of 50 pounds.
419.3.3 Spiral stairways. Spiral stairways that conform to the requirements of Section 1009.9 shall be permitted.
419.3.4 Locks. Egress doors shall be permitted to be locked in accordance with Exception 4 of Section 1008.1.9.3.
419.4 Vertical oenings. Floor openings between floor levels of a live/work unit are permitted without enclosure.
419.5 Fire protection. The live/work unit shall be provided with a monitored fire alarm system where required by Section 907.2.9 and an automatic sprinkler system in accordance with Section 903.2.8.
419.6 Structural. Floor loading for the areas within a live/work unit shall be designed to conform to Table 1607.1 based on the function within the space.
419.7 Accessibility. Accessibility shall be designed in accordance with Chapter 11.
419.8 Ventilation. The applicable requirements of the International Mechanical Code shall apply to each area within the live/work unit for the function within that space.
(Well, that's it folks, Enjoy)
Uncle Bob
(NEW Addition)
Exceptions: Live/work units complying with the requirements of Section 419 of the International Building Code shall be permitted to be built as one- and two-family dwellings or townhouses. Fire suppression required by Section 419.5 of the International Building Code when constructed under the International Residential Code for One- and two-family Dwellings shall conform to Section 903.3.1.3 of the International Building Code.
[F] 903.3.1.3 NFPA 13D sprinkler systems. Where allowed, automatic sprinkler systems installed in 0ne- and two-family dwellings and townhouses shall be installed throughout in accordance with NFPA 13D.
(Notes: Section 419, LIVE/WORK UNITS; of the 2009 IBC is also new

2009 IBC, Section 419, LIVE/WORK UNITS.
419.1 General. A Live/work unit is a dwelling unit or sleeping unit in which a significant portion of the space includes a non-residential use that is operated by the tenant and shall comply with Section 419. through 419.8.
Exception: Dwelling or sleeping units that include an office that is less than 10 percent of the area of the dwelling unit shall not be classified as a live/work unit.
419.1.1 Limitations. The following shall apply to all live/work areas:
1. The live/work unit is permitted to be a maximum of 3,000 square feet;
2. The non-residential area is permitted to be a maximum 50 percent of the area of each live/work unit;
3. The non-residential area function shall be limited to the first or main floor only of the live/work unit; and
4. A maximum of five non-residential workers or employees are alllowed to occupy the non-residential area at any one time.
419.2 Occupancies. Live/work units shall be classified as a Group r-2 occupancy. Separation requirements found in Sections 420 and 508 SHALL NOT apply within the live/work unit when the live/work unit is in compliance with Section 419. High-hazard and storage occupancies shall not be permitted in a live/work unit. The aggregate area of storage in the non-residential portion of the live/work unit shall be limited to 10 percent of the space dedicated to non-residential activities.
419.3 Means of Egress. Except as modified by this section, the provisions for Group R-2 occupancies in Chapter 10 shall apply to the entire live/work unit.
419.3.1 Egress capacity. The egress capacity for each element of the live/work unit shall be based on the occupant load for the function served in accordance with Table 1004.1.1.
419.3.2 Sliding doors. Where doors in a means of egress are of the horizontal-sliding type, the force to slide the door to it's fully open postion shall not exceed 50 pounds with a perpendicular force against the door of 50 pounds.
419.3.3 Spiral stairways. Spiral stairways that conform to the requirements of Section 1009.9 shall be permitted.
419.3.4 Locks. Egress doors shall be permitted to be locked in accordance with Exception 4 of Section 1008.1.9.3.
419.4 Vertical oenings. Floor openings between floor levels of a live/work unit are permitted without enclosure.
419.5 Fire protection. The live/work unit shall be provided with a monitored fire alarm system where required by Section 907.2.9 and an automatic sprinkler system in accordance with Section 903.2.8.
419.6 Structural. Floor loading for the areas within a live/work unit shall be designed to conform to Table 1607.1 based on the function within the space.
419.7 Accessibility. Accessibility shall be designed in accordance with Chapter 11.
419.8 Ventilation. The applicable requirements of the International Mechanical Code shall apply to each area within the live/work unit for the function within that space.
(Well, that's it folks, Enjoy)

Uncle Bob