Just wanted to make sure if I read this correct.
I have a mercantile occupancy with a total of 64 occupants, that makes for 32 males and 32 females.
Table 4-1 for Retail says 1:1-100 for males (1 toilet fixture for the first 100 males)
and 1:1-25 for females (1 toilet fixture for the first 25 females)
Having 32 female occupants I would need 2 toilet fixtures for females.
Am I reading this correct. (seems way too many in my humble opinion)
 
& ~ & ~ &

Yes, ...you are reading it correctly !
Also, refer to Section 412.5.1.


& ~ & ~ &
 
Note
The Later editions have altered the women's count lower

There sure is a need to revisit these fixture requirements.
When I see that for Office buildings the count for female toilets starts at 3 that appears ridiculous to me.
Even taking into account 412.3 that allows an exception for occupancies of less than 1,500 s.f. this still over the top in my humble opinion.
 
There sure is a need to revisit these fixture requirements.
When I see that for Office buildings the count for female toilets starts at 3 that appears ridiculous to me.
Even taking into account 412.3 that allows an exception for occupancies of less than 1,500 s.f. this still over the top in my humble opinion.
They Have, update to the 2015UPC
 
There are more and more women in the workplace every day.
I agree. But imagine an office space of 1,600 s.f. That accounts for 16 occupants, 8 male and 8 female.
The 2009 UPC would require 1 toilet plus 1 urinal for male and 3 female toilet fixtures.

The 2009 IBC only requires 1 male and 1 female toilet which appears adequate to me considering the office use of such a space.
 