804.4.1 Minimum critical radiant flux. Interior floor finish and floor covering materials in exit enclosures, exit passageways and corridors shall not be less than Class I in Groups 1-2 andR-2.1 and not less than Class II in Groups A, B, E, H, 1-4, L, M, R -1, R -2 and S. In all areas, floor covering materials shall comply with ASTM Standard E 648, and having a specific optical density smoke rating not to exceed 450 per ASTM E 662.Exception: Where a building other than a Group 1-3 is equipped throughout with an automatic sprinkler system in accordance with Section 903.3.1.1 or 903.3.1.2, Class II materials are permitted in any area where Class I materials are required, and materials complying with ASTM < Standard E 648, and having a specific optical density II smoke rating not to exceed 450 per ASTM E 662 are permitted in any area where Class II materials are required.