BACKGROUND:
I have an existing non-permitted 1,721 sf physical therapy/office space in CA, which we are preparing plans to legalize. The space has a single uni-sex restroom (non-ada compliant), 3 offices, reception, utility room and 658 sf of exercise area "gym". The area is calculated using inside of exterior walls.
The plan checker thinks two restrooms are needed, one for each sex. He's agreed not to classify the "gym" as an A group.
Per Table A the Occupant Load Factor for Group B or I is 200: (B being the closest group to the actual facility)
1,721sf/200 = 8.6, call it 9
Using 2010 CPC Chap 4, sec 412.3 Separate Facilities, Exception 2 - In occupancies serving 10 or fewer people (occupant load) one unisex restroom is permitted.
Our load is less than 10, thus the existing ui-sex restroom should be permitted - CORRECT??
Also, when determining the Load factor can walkways or paths of travel in a space that has no constructed corridors be eliminated when determining the area, since these are "accessory" spaces like a restroom, corridor or space beneath stairs?
I appreciate your responses.
-Saul
I have an existing non-permitted 1,721 sf physical therapy/office space in CA, which we are preparing plans to legalize. The space has a single uni-sex restroom (non-ada compliant), 3 offices, reception, utility room and 658 sf of exercise area "gym". The area is calculated using inside of exterior walls.
The plan checker thinks two restrooms are needed, one for each sex. He's agreed not to classify the "gym" as an A group.
Per Table A the Occupant Load Factor for Group B or I is 200: (B being the closest group to the actual facility)
1,721sf/200 = 8.6, call it 9
Using 2010 CPC Chap 4, sec 412.3 Separate Facilities, Exception 2 - In occupancies serving 10 or fewer people (occupant load) one unisex restroom is permitted.
Our load is less than 10, thus the existing ui-sex restroom should be permitted - CORRECT??
Also, when determining the Load factor can walkways or paths of travel in a space that has no constructed corridors be eliminated when determining the area, since these are "accessory" spaces like a restroom, corridor or space beneath stairs?
I appreciate your responses.
-Saul