pleach assuming the decking is on the roof and not an exterior wall projection I would recommend using Section 1501.1 (2012 IBC) and other sections in the code that are applicable i.e. Chapter 7.
Postscript: 2015 IBC
[BF] 1505.1 General. Roof assemblies shall be divided into the classes defined below. Class A, B and C roof assemblies and roof coverings required to be listed by this section shall be tested in accordance with ASTM E108 or UL 790. In addition,
fire-retardant-treated wood roof coverings shall be tested in accordance with ASTM D2898. The minimum roof coverings installed on buildings shall comply with Table 1505.1 based on the type of construction of the building.
Exception: Skylights and sloped glazing that comply with Chapter 24 or Section 2610.
Commentary: The code designates the use of any particular classification of roof coverings based on the type of construction of the building. A minimum Class B roof covering is required for all roofs that have a minimum 1-hour fire-resistance rating in accordance with Table 602. Roofs without a required fire-resistance rating require a minimum Class C roof covering.

a. Unless otherwise required in accordance with the
International Wildland- Urban Interface Code or due to the location of the building within a fire district in accordance with Appendix D.
b. Nonclassified roof coverings shall be permitted on buildings of Group R-3 and Group U occupancies, where there is a minimum fire-separation distance of 6 feet measured from the leading edge of the roof.
c. Buildings that are not more than two stories above grade plane and having not more than 6,000 square feet of projected roof area and where there is a minimum 10-foot fire-separation distance from the leading edge of the roof to a lot line on all sides of the building, except for street fronts or public ways, shall be permitted to have roofs of No. 1 cedar or redwood shakes and No. 1 shingles constructed in accordance with Section 1505.7.