I have a project in Wisconsin, using IBC 2015 (with amendments), in an existing mixed S-1/B occupancy which is roughly 30,000 sq. ft., 1 story, unsprkinklered.
A proposal is to change a portion of the building (10,000 Sq. Ft.) to be separated and will include a change of use (to A-3). It isn't the full 10,000 sq. ft., but the separation would include all occupancies not otherwise separated.
IEBC 1012.1.1.2 - 2015 - makes it clear in the commentary that if separated by fire barriers per IBC 508.4, then only that portion needs to comply (with the various referenced sections). The commentary also includes the phrase "this shall also apply to exceeding IBC chapter 9 thresholds".
Here's the question:
1) IBC 508.4 requires only a 2-hour wall between the A-3 space and the S-1 space (worse case). IBC 707.3.10 would require a 3-hour barrier to be separate fire areas. If the 2-hour barrier is provided, does the A-3 space need to have a sprinkler installed, or not? The "Fire area" is more than 12,000 sq. ft. (per IBC 903), but the change-in-use area is separated per 508.4 and is less than 12,000 sq. ft. on its own. Intent is to avoid sprinklers.
2) If the barrier would be a 3-hour barrier, sprinklers would not be required for the work area. However, the commentary on IEBC 1012.1.1.2 makes it seem the higher-level barrier may not be needed.
A proposal is to change a portion of the building (10,000 Sq. Ft.) to be separated and will include a change of use (to A-3). It isn't the full 10,000 sq. ft., but the separation would include all occupancies not otherwise separated.
IEBC 1012.1.1.2 - 2015 - makes it clear in the commentary that if separated by fire barriers per IBC 508.4, then only that portion needs to comply (with the various referenced sections). The commentary also includes the phrase "this shall also apply to exceeding IBC chapter 9 thresholds".
Here's the question:
1) IBC 508.4 requires only a 2-hour wall between the A-3 space and the S-1 space (worse case). IBC 707.3.10 would require a 3-hour barrier to be separate fire areas. If the 2-hour barrier is provided, does the A-3 space need to have a sprinkler installed, or not? The "Fire area" is more than 12,000 sq. ft. (per IBC 903), but the change-in-use area is separated per 508.4 and is less than 12,000 sq. ft. on its own. Intent is to avoid sprinklers.
2) If the barrier would be a 3-hour barrier, sprinklers would not be required for the work area. However, the commentary on IEBC 1012.1.1.2 makes it seem the higher-level barrier may not be needed.